suggetion. make your new 2.5 into 2 radials, say 4 sockets apiece, feed each with a fused 13A spur off the 4mm radial. then you,ve still got 32A cct. in first room

That's what I would do but I should advise you that if this is a dwelling you need to be registered under a competence person scheme or you need to notify building control to get them sign to it off, dwelling or not I would seriously suggest you get a the on-site guide and familiarise yourself with the current regs especially those regarding earthing and bonding, have you even establihed the supply characteristics ? Not to mention you will need test instruments to measure Ze,PFC, and Zs for your final circuits as well as all the other verification tests required..Good luck dude
 
That's what I would do but I should advise you that if this is a dwelling you need to be registered under a competence person scheme or you need to notify building control to get them sign to it off, dwelling or not I would seriously suggest you get a the on-site guide and familiarise yourself with the current regs especially those regarding earthing and bonding, have you even establihed the supply characteristics ? Not to mention you will need test instruments to measure Ze,PFC, and Zs for your final circuits as well as all the other verification tests required..Good luck dude


As long as the anticipated load is within the limits of the protective device there is no reason why the circuit cant be a 20a radial,although it may exceed the recommended floor area of 50sqm...this is a recommendation not a requirement.
If the alteration to an existing circuit does not involve alterations in a kitchen or bathroom it does not come under part P and so no requirement to register with BC......and you do not need to be registered with a competant person scheme,any Tom,Dick or Abdul can legally extend or alter an existing circuit not in a kitchen or bathroom, or outside without carrying out any tests or inspections,they can wire it in a bit of wet string if they want.....doesnt make it right but thats the way it is.
 
I still think it's notifiable..

because... Work NOT in a special location or Kitchen is NOT notifiable unless you satisfy note (f) page 21 Electricians guide to Building regs I don't believe it is in it's present form, and by changing the protective device at source I think it's on thin ice. Just my opinion.

ATB Steve
 
........any Tom,Dick or Abdul can legally extend or alter an existing circuit not in a kitchen or bathroom, or outside without carrying out any tests or inspections,they can wire it in a bit of wet string if they want.....doesnt make it right but thats the way it is.

Don't agree with this bit, either, Wirepuller - are you having a bad day??:)

If the OP had done what he originally planned (extended ring by 8 socket outlets), or added the radial to the existing ring, then of course he would be required to do a full set of tests - all the parameters will have changed: Zs, R1 + R2.....and he'd have to IR test.

And you couldn't call it 'minor works' - that would be a stretch of anyones imagination - so would require an EIC, Schedule of Inspections and a Schedule of Test results.......regardless of whether it's 'notifiable' or not.:)
 
Last edited by a moderator:
1.4 of Electricians guide to Building Regs clearly states..The technical requirements of Part P shall apply to all electrical installation work in dwellings whether the work is notifiable or not.

So seeing as the regs book is the substance of the Part P work that clearly means a full EIC. I agree with Wayne.
 
Don't agree with this bit, either, Wirepuller - are you having a bad day??:)

If the OP had done what he originally planned (extended ring by 8 socket outlets), or added the radial to the existing ring, then of course he would be required to do a full set of tests - all the parameters will have changed: Zs, R1 + R2.....and he'd have to IR test.If he is an electrician,yes....if he is not...no.

And you couldn't call it 'minor works' - that would be a stretch of anyones imagination - so would require an EIC, Schedule of Inspections and a Schedule of Test results.......regardless of whether it's 'notifiable' or not.:)Incorrect....a minor works will cover an alteration or addition to one existing circuit,no matter how extensive

If an existing circuit is extended...even considerably by 8 sockets then that is minor works,and a minor works cert would suffice,although I accept I was incorrect in that if the protective device was changed then the work would be notifyable. Even if the protective device was changed as long as the alteration was to an existing circuit that would still be covered by a minor works cert,an EIC would not be required.
If the work is not notifyable anyone can do it in any way they please and not carry out any tests or provide any certs....Bs 7671 is not statutory and and part P does not apply to many installs.
If the OP was a qualified electrician then he would be negligent not carrying out a full test,if he is a DIYer he can do whatever he likes.
 
Last edited by a moderator:
If an existing circuit is extended...even considerably by 8 sockets then that is minor works,and a minor works cert would suffice,although I accept I was incorrect in that if the protective device was changed then the work would be notifyable. Even if the protective device was changed as long as the alteration was to an existing circuit that would still be covered by a minor works cert,an EIC would not be required.
If the work is not notifyable anyone can do it in any way they please and not carry out any tests or provide any certs....Bs 7671 is not statutory and and part P does not apply to many installs.
If the OP was a qualified electrician then he would be negligent not carrying out a full test,if he is a DIYer he can do whatever he likes.

Sorry, Wirepuller, cannot accept this statement - and very misleading for others reading this thread.

A MEIWC is for the addition of a socket outlet, or a lighting point, to an existing circuit, or similar works - not to extend a 'Ring Final' to encompass a new room with 8 socket outlets.

Tell me, where on the Minor Works Certificate would you fill in your 'Ring Final' test results?

And what is the 'tick-box' on an EIC for that says 'Alteration to an Existing Installation', if not for a job like this one?


GN3, Pg 96 - MEIWC Scope

The Minor Works Certificate is intended to be used for additions and alterations to an installation that do not extend to the provision of a new circuit. Examples include the addition of a socket outlet or a lighting point to an existing circuit, the relocation of a light switch etc. This certificate may also be used for the replacement of equipment such as accessories or luminaires, but not for the replacement of distribution boards or similar items. Appropriate inspection and testing, however, should always be carried out, irrespective of the extent of the work undertaken.

Also,

GN3, Pg 98 Guidance For Recipients

A seperate Certificate should have been received for each existing circuit on which the minor works have been caried out.
This certificate is not appropriate if you requested the contractor to undertake more extensive installation work, for which you should have received an Electrical Installation Certificate.

So I think a MEIWC is not appropriate in this instance and all rellevant tests should be carried out and recorded on the 'Schedule of Test Results':)
 
"The Minor Works Certificate is intended to be used for additions and alterations to an installation that do not extend to the provision of a new circuit. Examples include the addition of a socket outlet or a lighting point to an existing circuit, the relocation of a light switch etc. This certificate may also be used for the replacement of equipment such as accessories or luminaires, but not for the replacement of distribution boards or similar items. Appropriate inspection and testing, however, should always be carried out, irrespective of the extent of the work undertaken"

The section of your quote I have highlighted is relevant in this instance.....For alterations to an existing circuit an EIC is a sledgehammer to crack a nut. You state that where is the provision for recording ring continuity results?...well the same applies if you add one socket to a ring as well as eight...are you going to do an EIC for one socket which you have extended the ring to install?I If you wish to record ring continuity results you can use the comments box.
Let me make it clear that I am NOT advocating that tests on this sort of install need not be carried out,of course they should and an appropriate cert completed,,(minor works)....The point I was making is that legally,anyone can do this sort of install with no tests or certs,because very often it does not come under part P.
I will state catagorically that I have been using minor works forms for just this sort of install for the 15 odd years we have been NIC,,,and on our yearly inspection this has never been queried.
Minor works is relative anyway....8 sockets added to an existing circuit in a one bed flat may seem major....but in a large commercial premises 8 additional sockets added to a legnth of dado trunking is minor.Do an EIC for a minor job on such premises and you will have to carry out inspections and tests to verify supply characteristics at the intake/main switch type/main fuse type/Ze/psc/....if the DB serving the circuit is a sub board you will need the same for that as well......ridiculous for a simple addition to an existing circuit......a sledgehammer to crack a nut.
 

Reply to 2.5mm radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
736
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
333
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top