Hello all !!

Situation - 100A DNO fuse in house no 1, running CU in house no 1 -
home owner wishes CU in house no 2 to be run from the same DNO fuse,
the CU in house no 2 has 3 x 6A lighting circuits and 2 x 32A ring circuits,
and they want a shower to be installed, but haven't specified the kw rating, so assume 8.5kw and 40A mcb.
What size tails should be run to house no 2?
The cable run from house to house is 10m.
25mm tails?

Thanks !!

:) :) :)
 
You need to fit a KMF after a Henley to feed a 16mm sub (probably needs to be SWA). Earthing requirements will dictate the rest.

Anything else you need to be spoon fed?
 
What size are the tails currently on house number 1? If they are 16mm then an extra 47A (approx max demand) from house number 2 is certainly pushing the limits.
 
Hi - thanks for all the replies! :)

Happyhippydad - I don't know what size the first house tails are, but will be investigating - am hoping they are 25mm.

Murdoch - it's cost, you're right Wozz! There are two standing charges, one for each property, and there are solar panels across both properties but only benefitting one supply.

Hawk - it will be metered from the first house, as the tails will be leaving after the meter.

Thanks, Rockingit.

I'd be happier if they weren't fitting the shower, load-wise, as the rest of the installation is pretty low on load.

Cheers guys!!

:smile5: :martini_shaken::26::54::yes:
 

Reply to 2 Consumer Units run from one 100A DNO fuse - cable size? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
370
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
335
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
372

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
667
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
448

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top