QUOTE=Canoeboy;208748]Did you read the correct column as the figure I have is different ?

I may have missed something but I hope the attached is correct and answers your question.


View attachment armour.pdf
 
Last edited:
QUOTE=Canoeboy;208748]Did you read the correct column as the figure I have is different ?

I may have missed something but I hope the attached is correct and answers your question.


View attachment 3307

You haven't missed anything as such but the table only indicates a non-compliance with table 54.7 whereby you can then use the adiabatic equation to size your cpc which invariably results in a lower required CSA by calculation.
 
You haven't missed anything as such but the table only indicates a non-compliance with table 54.7 whereby you can then use the adiabatic equation to size your cpc which invariably results in a lower required CSA by calculation.

Yes you can use the adiabatic equation but I was asked where my figure of 49.74 came from. The table will not give the most economical solution in all cases but it is an easy reference chart and always works on the side of caution. This means that at least your CPC will not be undersized. You would still be advised to use the equation to check though.
 

Reply to 2 core armored cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
757
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

No table I just know the conductivity of the armour is around 4.0mm² copper equivalent so 6.0mm² will be fine.
Replies
6
Views
452
What readings were you expecting for the cable prior to testing? What is the make of the protective device? Is there any previous paperwork [test...
Replies
3
Views
459

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top