Jberry

-
Joined
Apr 10, 2019
Messages
15
Reaction score
2
Location
Westmeath
This unit is running two showers. Unit was smoking while one shower was running, never tripped the safety switch. Power to one shower is cut off while the other is in use. Is it ok just to change out the relay that had burned? I'm not an electrician but one will be doing the work. The house is rented and the landlord will be arranging the repairs but I'm afraid he probably wont send someone who's registered

[ElectriciansForums.net] 2 electric showers and melted live wire from relay


[ElectriciansForums.net] 2 electric showers and melted live wire from relay
 
ABB Switchgear is very good.

All that needs is a 230v coil, n/o contactor rated 40A or above. They come with 4 pole but only use 2. It's suitably protected against overload by the 40A MCB. That has overheated either due to contactor failing or poor termination. Just get the contactor and damaged wiring replaced.

Any reason why the power never cut to it?
 
ABB Switchgear is very good.

All that needs is a 230v coil, n/o contactor rated 40A or above. They come with 4 pole but only use 2. It's suitably protected against overload by the 40A MCB. That has overheated either due to contactor failing or poor termination. Just get the contactor and damaged wiring replaced.

Any reason why the power never cut to it?
The smoking will have been caused by the overheating of the conductor and the consequential burning of the plastic insulation (most likely due to a poor termination). It's unlikely any of the protective devices would trip because electrically the only fault appears to have been a bad termination, there doesn't appear to have been any unwanted connections say between live and neutral or earth which would cause the devices to trip.

Basically it looks like a simple case of bad workmanship when it was installed, but as I said, definitely not the first time this has happened.

As for you wanting to see paperwork from the electrical contractor (I use the term loosely based on what you've said), you're not the person ordering the work so technically you've got no right to see the paperwork.


Thanks for the detailed answer. As for paperwork I really just want to make sure that he doesn't send over someone who has no electrical expertise at all. As he has already done. He sent over someone I knew well and so knew they didnt have the knowledge
 
Any reason why the power never cut to it?
Hi - the 40A MCB is designed to not trip at 40A, it's ok with that load. Your 9.5kW shower will draw approx 9500/240 = 40A . So unless both showers went on at once (or some other fault) the MCB will run happily. That contactor is rated at 40A so it should be ok, but it is on its rated max and they do have an operational life limit. From the pics ( :eek: ) I suspect a poor termination has caused the overheating, as per @SparkyChick.
 

Reply to 2 electric showers and melted live wire from relay in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
593

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top