Would that statement be untrue if all the conductors are rated at the highest voltage? only asking.If it is a central system you will not be able to use the same cable, segregation will be required.
No for central systems segregation must be applied.Would that statement be untrue if all the conductors are rated at the highest voltage? only asking.
No for central systems segregation cheers thanks for that Westymust be applied.
Part of Reg 8.2.6, BS5266:1. Where multi-core cable is used for the emergency lighting, none of the conductors should be used for any other circuit.
I take it that this applies if he is still going with the emergency power pack remote. I think self-contained is a better option.He cannot run them in one cable anyhow
Is the person coming up with the ideas aware of all the options?I personally agree that self contained is a better option.
For me I wanted clarification in regards to the idea as I am not the one who is coming up with the idea.