lee foster

Hi , I have a PV job that requires 2 inverters due to different array orientations , each array will be 1715kWP , can i put both inverters on the same AC circuit as betwen them they are under 16A? or do ineed to run a circuit for each inverter?.
Thanks in advance.

Lee
 
Surely Wp, Mr Watt might be offended!


And the inverters could probably go on the same circuit if all the wiring is rated for 16A, but make sure each has its own AC isolator.

John
 
Hi John , Wp absoloutley correct , thanks for the help think i'll go for the 1 AC Circuit with seperate isolation.

Thanks again much appreciated.

Lee
 
I would check that you can do that. My understanding is that every cable needs its own protective device, unless they are parralell feeds to the same loads ???

In any event a small sub board with 2 x 10a MCS would do it.
 
As well as sizing all the cables for 16A you also need to check the maximum fuse/mcb rating of the individual inverters as this may be less, in which case it's the sub-board...
 
If you run them both into their own isollators, then join the AC cables that connects them in parallel, adding the 2 current levels together but keeping the voltage the same. no problem putting them both on the same MCB as it's under 16A and they are radial circuits.
 
Thanks for the replies , i'm going to check with the Manufactuer of the inverters , hopefully they can clear it up for me.

Thanks again

Lee
 
What inverters are you using ?
most of the manufacturers advice I've seen specifies that each string inverter should be on its own Mcb

(I'm thinking that you are trying to use one meter for both inverters , if this is the case I would run tails from Henley block to a main switch through the meter to a two way consumer unit then to two Isolators one for each circuit/inverter)

also in the Dti guide it says ''An inverter supplied from a Pv array must preferably be installed in a dedicated circuit''
 
Last edited:
Hi edexlab , Mastervolt inverters as i can't get SMA at the moment , i think i'm just going to put 2 radials in and be done with it , the C/U is only a couple of meters away from the inverter location anyway , would you consider 2 meters one for each inverter?.

Thanks for the info.

Lee
 
The other thing to consider is redundancy, if two inverters are fed from one MCB, and one faults, you lose both inverters.

As for radial circuits, does this only apply to fixed equipment that's fed from a fused spur or socket?
 
There is no need to fuse down a radial circuit to feed sockets using a SFS, you can just use an isolator, you can run any number of 'spurs' from a radial circuit which can be taken at any point along it's length, including at the consumer unit. There are of course the issues of demand and floor area to consider though.

Other wise I think it depends on your interpretation. I would regard the solar array as a single installation, even if it has 2 inverters and 2 strings, so feeding both from one MCB is acceptable, but I think that is open to interpretation.
Otherwise you would need 2 meters as well and theoretically I could see a problem with this then being considered as 2 installations at the same address.
 
Surely one circuit is fine. Apart from anyone's interpretation of the DTI guide can anyone think of any reason why not?

The earlier comment about if an inverter has a fault you will lose both is a bit questionable. How often will thus happen and surely you will just turn the isolator off for the faulty inverter?
 

Reply to 2 inverters in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top