Discuss 2 k ohm between L+E on lighting circiut in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

daiplayer

Is this a fault ? shouldnt resistancebetween live and nuetral be greater than this at the board ? (lightind circiut) some spot bulbs in (230v)....
 
You should have all bulbs removed before testing insulation resistance on a lighting circuit and ensure any fluo lights are disconnected
 
say that the op does this to his cct how would this reading make any diffrence for example if a bulb is still pluged in?

Because you don't physically pass a voltage between L+N -they remain at the same potential.

To the OP:

What is the earth system, are there any rcd's and have you got all cables for that circuit removed from the DB?

I'm concerned that you're asking if a reading of 0.002 MOhms is a fault!
 
Last edited:
ahh i see cheers for tht IQ, the op said Kohms not Mohms am i correct in saying tht under 1Mohm is below the required reading by the bs7671
 
ahh i see cheers for tht IQ, the op said Kohms not Mohms am i correct in saying tht under 1Mohm is below the required reading by the bs7671

Yes, correct and if the OP is correct then he has a reading of 0.002 MOhms
 
what im saying is tht the tester my boss uses is a megger mft 1553 and when testing IR it never says Kohms or i have never seen it. it only says eg 0.02Mohms or >299M ohms

when conducting R1+R2 when there is a loose connection ect the reading will be 2.3Kohms ???
 
Is this a fault ? shouldnt resistancebetween live and nuetral be greater than this at the board ? (lightind circiut) some spot bulbs in (230v)....

Look at what you've written....

If you're talking R1+R2 then why would you want a greater resistance when less is better?

Then, you're on about testing on the MOhm scale of an insulation resistance tester, I've done all I can here!
 

Reply to 2 k ohm between L+E on lighting circiut in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top