true, first thing you should do before testing any lighting circuit, isolate it , remove all lamps and sensitive equipment out of the circuit, to avoid suspect readings, common procedure realy.......
 
if you do a continuity test on conductors that , in design, should not be in contact...then a high reading should show...if low ohmmeter (which is what these basically are) reading are found , then it shows continuity between conductors that should not be in contact. same thing, but using it in a different way.

Insulation tests are designed to check between conductors that should in design not be in contact

Continuity tests are designed to check between conductors that should be in contact.

Both are ohmmeters, just different design.
 
If there are fluorescent lights on the circuit you will need to disconnect them rather than just remove the lamp.

Edit....thats already been said.
 
Last edited by a moderator:
One thing thats not been mentioned is you should realy disconnect the neutral from the board when doing IR tests as you could get false readings especially on a TNCS system where the earth and neutral are linked
 
One thing thats not been mentioned is you should realy disconnect the neutral from the board when doing IR tests as you could get false readings especially on a TNCS system where the earth and neutral are linked

I asked that in post 9
 

Reply to 2 k ohm between L+E on lighting circiut in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top