true, first thing you should do before testing any lighting circuit, isolate it , remove all lamps and sensitive equipment out of the circuit, to avoid suspect readings, common procedure realy.......
if you do a continuity test on conductors that , in design, should not be in contact...then a high reading should show...if low ohmmeter (which is what these basically are) reading are found , then it shows continuity between conductors that should not be in contact. same thing, but using it in a different way.
Insulation tests are designed to check between conductors that should in design not be in contact
Continuity tests are designed to check between conductors that should be in contact.
Both are ohmmeters, just different design.
If there are fluorescent lights on the circuit you will need to disconnect them rather than just remove the lamp.
Edit....thats already been said.
One thing thats not been mentioned is you should realy disconnect the neutral from the board when doing IR tests as you could get false readings especially on a TNCS system where the earth and neutral are linked
I asked that in post 9
Reply to 2 k ohm between L+E on lighting circiut in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...