2 methods of obtaining Ipf? | on ElectriciansForums
Discuss 2 methods of obtaining Ipf? in the Electrical Course Trainees Only area at ElectriciansForums.net
Birmingham
got a question in my assignment but unsure how to do it as i havent had much experience testing. any help appreciated.
id say by doing the calculation Ze / voltage but also by doing it with the tester.. basic knowledge i know but any of what i said correct? lol
You're nearly right on one method of acquiring Ipf. You can calculate it using measurements as you've stated, but the maths is I=V/R so U0/Ze, but that will only give you the prospective earth fault current (L-E fault), which may be less than the prospective short circuit current (L-N fault). So to calculate it, you would need to measure the L-N loop impedance, do another calc and use whichever is higher.
This is for single phase, 3 phrase is different.
So, measurement/calculation is one method of obtaining it. There is another method for obtaining it. What might that be?
what would the L-N fault calc be? and i would say by phoning up the supplier! but not exactly sure about that as they probably wouldnt know
The L-N fault calc is the same (I=V/R). You measure the loop impedance across L and N on the incomer, and divide U0 by that value. That will give you the prospective short circuit current.
And you're bang on with the second method.
So, measurement/calculation and enquiry :)
Measuring it is correct, what test and type of instrument would be used?
Calculating it is also another method as you said, V=IR therefore I = V/R in this instance V=Uo and R=Ze.
There is one final way of obtaining an Ipf however I think (I may be wrong someone please correct me if so) it may be a bit more of a generic value for the area. That's a huge hint for you.
The OP has already mentioned enquiry if that's what you're meaning
Perhaps he means the guidance that except in large city centres the fault current is not likely to exceed 16kA; and so a consumer unit to BS61439-3 which is type tested to 16kA could be used (subject to the origin protection type) (Annex ZB).
However this is a bit of a bypassing the issue approach, but it is probably what you would get if you managed to get a response to your enquiry.
When doing the calc is it always best to use nominal voltage or the voltage the system is actually operating on?
You should use the stated nominal voltage of the supply. This is constant. The actual supply voltage is changing constantly as a result of the ever changing supply/demand characteristics of the grid.
As a bonus, the ever changing supply voltage is why you can't realistically measure voltage drop using a voltmeter (measure at the origin, then by the time you measure at the end of the circuit, the supply voltage is likely to have changed).
Reply to 2 methods of obtaining Ipf? in the Electrical Course Trainees Only area at ElectriciansForums.net
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Hi I've nearly completed the 2357 NVQ. I'm just a bit stuck with Permits to work, Planned program of work and method statements. I work in the...