You're nearly right on one method of acquiring Ipf. You can calculate it using measurements as you've stated, but the maths is I=V/R so U0/Ze, but that will only give you the prospective earth fault current (L-E fault), which may be less than the prospective short circuit current (L-N fault). So to calculate it, you would need to measure the L-N loop impedance, do another calc and use whichever is higher.

This is for single phase, 3 phrase is different.

So, measurement/calculation is one method of obtaining it. There is another method for obtaining it. What might that be?
 
The L-N fault calc is the same (I=V/R). You measure the loop impedance across L and N on the incomer, and divide U0 by that value. That will give you the prospective short circuit current.

And you're bang on with the second method.

So, measurement/calculation and enquiry :)
 
Measuring it is correct, what test and type of instrument would be used?

Calculating it is also another method as you said, V=IR therefore I = V/R in this instance V=Uo and R=Ze.

There is one final way of obtaining an Ipf however I think (I may be wrong someone please correct me if so) it may be a bit more of a generic value for the area. That's a huge hint for you.
 
Perhaps he means the guidance that except in large city centres the fault current is not likely to exceed 16kA; and so a consumer unit to BS61439-3 which is type tested to 16kA could be used (subject to the origin protection type) (Annex ZB).
However this is a bit of a bypassing the issue approach, but it is probably what you would get if you managed to get a response to your enquiry.
 
You should use the stated nominal voltage of the supply. This is constant. The actual supply voltage is changing constantly as a result of the ever changing supply/demand characteristics of the grid.

As a bonus, the ever changing supply voltage is why you can't realistically measure voltage drop using a voltmeter (measure at the origin, then by the time you measure at the end of the circuit, the supply voltage is likely to have changed).
 

Reply to 2 methods of obtaining Ipf? in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top