If i have a sub main do i have to do 2 eic certs or the 1 and when i get to circuit details write in the sub main circuits.
Im thinking 2 as u can then put in the supply characteristics from the main ccu?
 
As far as I am aware you just need 1 IEC and 2 schedule of test results.
The first test results page will show Ze at incomer, and Zs from main switch at sub main (recorded as distribution circuit).
The second test results page then has the previous Zs figure as the Ze figure, with R1+R2 of circuits added to give a final Zs.

Although the second test sheet says Ze its sometimes refered to as Zdb.
Hope that helps and makes sense.
 
When running a submain from the intake position, all the details are recorded as normal at the intake, Ze, pfc etc.

Then at the CU you treat the submain feeding that, as a circuit, but, depending on who your scheme provider is, you record the Ze at the cu, (or in this case would be Zs for the submain) in the relevant box.

Top line of the cert will be your sub main, then underneath, record the CU circuits details as normal.
 

Reply to 2 or 1 certs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
268
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
755

Similar threads

We wouldn't be at all surprised I have been a QS for 25 odd years.
Replies
7
Views
814
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top