gibbyisking

hi guys.

right i'm doing a kitchen next week and the customer has got 2 ovens (both 3.8kW) and a induction hob (10.8kW).

The hob will be on its own circuit with a 10mm T&E supply.

As for the 2 ovens. I have the possibilty to supply both of these with a 6mm T&E but all they need is a 20A DP switch. I thought about changing it to either 4mm or 2.5mm. Whats your thoughts guys?

One of the ovens has a plug and the oven I have to put the cable in for it
 