3 core SWA used to power a sub board N and 2 phases SWA as CPC, I said to the customers engineer that I have linked the two MCB,s so that in the event of a fault or for maintenace both phases will disconnect together, No dont want that he said dont need to be, ok I said you can alter it after I have signed it off, linked and sealed MCB,s and took a pic, Am I right comments guys and girls
Pict
 
Without knowing the nature of the load it’s hard to say anything about this setup. If there are DP loads then the incoming switch / MCB must break all phases and neutral with the proviso that the neutral must be late break.

With resistive loads then In = √((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic))) where Ic=0. For inductive loads where harmonics in the neutral cause a rise in current above the natural triplen you will have problems with the neutral conductor.
 
Ime assuming this is a 2 phase load such as a 110v DP (55v each phase) supply?

If so the breaker has to disconnect both phases at the same time same as you would for a 3phase supply.
 
OK L1 L2 are supplied from the main board to L1 L2 on the sub L1 supplies a washer and L2 a dryer B32 4 mm radial, a light circuit 4 florrys B6 lights are on the same phase as washer, I have linked the breakers in the main board so that both phases disconnect together, I mean would you de link a 3 phase breaker I think not, if your working on the sub wouldn't you want both isolated ? I would so they are linked in case some clown only reads one breaker and thinks, ok thats the laundry board isolated,
Pict
 
I agree. I'd want a common point of isolation, although technically it's not required. Think of the old Bill fuse boards for example, 3 fuses would need to be pulled for one TP circuit.

As the phases are 120 degrees apart, then neutral currents aren't an issue.
if the two lives were on the same phase, then I'd have an issue with that.
 
Last edited:
Ime a little confused, Why have you put a 2 phase sub board in?
I could understand it if you needed it for a double pole load but as you are feeding single phase loads I dont see the benefit?
 
Pict, maybe you should have just used a 3P breaker.
I'm assuming the 2 phases are 120[SUP]o[/SUP] apart, so Tony's post no 5 could well be of some importance.
 
All considerations mentioned have been taken into account, it is only the question of isolation, I am insisting on as johnboy put it a "common point of isolation"
Pict
 
I agree. I'd want a common point of isolation, although technically it's not required. Think of the old Bill fuse boards for example, 3 fuses would need to be pulled for one TP circuit.

As the phases are 120 degrees apart, then neutral currents aren't an issue.
if the two lives were on the same phase, then I'd have an issue with that.


Wrong, just so wrong.
 
All considerations mentioned have been taken into account, it is only the question of isolation, I am insisting on as johnboy put it a "common point of isolation"
Pict

I doubt very much whether ALL considerations have been taken into account.

List what you have considered then we can see if you have considered all you should have in your design.
 

Reply to 2 Phase install in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
What readings were you expecting for the cable prior to testing? What is the make of the protective device? Is there any previous paperwork [test...
Replies
3
Views
462

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top