do you have 2/3 of a 3ph or 2 x incoming singles or a 1ph 3 wire (2x singles inverted off the same transformer)?? More info reqd.
In the UK, two phase is most often found on construction sites, the 110V yellow transformers.
There will be 55V on each conductor, so although the wiring colours sugest that there is a Line and Neutral, in fact both conductors are phase conductors.
In the states, they often use a system where each phase is 110V, and for items of equipment that require 220V, they use two 110V phases.
The phases are generally 180° apart, as oposed to 3 phase where the phases are 120° apart.
Its the same as any three phase supply. You get 3 Phase conductors and a neutral. 400V between phases or 230V to earth. Where as in a "split Phase" system you get 2 phase conductors and neutral. 480V between phase conductors, or 240V to earth.
the centre tapping is taken to earth, which also acts as the neutral conductor.
Reply to 2 phase in the Australia area at ElectriciansForums.net
Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back...