Hi all.

I’m currently wiring an S-Plan heating system (normally don’t get involved in this, but it’s been dumped on me).

I’m using a Honeywell DT90E room stat, and a Honeywell V4043H 2-port valve. In the room stat I’ve got A as live in, and B as live out (C not used, neutral not required), which is connected to the brown of the 2-port valve.

I’ve got 230v across the live and neutral of the valve, but the valve isn’t operating. The plumber who installed the system said to use A and C on the room stat, but what difference would this make to the supply of the valve? The DHW side works fine, it’s just the heating side that I’m having issues with.:banghead:
 
Switched live to the brown of the valve opens it. Permanant live to the grey switches the orange when valve opens and brings in pump/boiler.If you have 230v on the brown/blue it should open regardless of other connections.
 
If you have 230v on the brown/blue it should open regardless of other connections.

Thats what I thought. But its also the fact that the plumber said to use terminal C (diagram didn't show any cables connected), so he knows what connections there are in the room stat.

What would happen if I reversed the brown valve cables, so the hot water demand operated the heating valve to see if it works?
 
The valves are a bit of a pain to get too, so the changing wires over option might be better. Its just to see if the valves operate, if they do, then I think there might be an issue with the room stat?:icon9:
 
Do you have 230v on the call for heat from the roomstat,you said a is common and b is call so 230v should be on the brown of the htg valve,measure in the wiring centre,is the neutral going to the valve(i have known a broken neutral before which shows the same problem,remember that as both oranges are connected to the switched live for boiler that you will get feed back from the other valve(90v or something even when hw is not calling.
 
Thats what I don't understand? Ive got 230v across the brown and blue of the valve, when the stat clicks in, but the valve does nothing.....just sits there! Even when I manually open the valve using the little slide lever on the side, it doesn't bring in the boiler?
 

Reply to 2-Port valve wiring? in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Certainly is!! And another thing .......... On the old Hive receiver the relay common is a separate terminal, whereas on the new Hive presumably...
Replies
5
Views
408
I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top