Hi all

I'm using a fluke multimeter and when i test insulation resistance i get a reading of about 300Mohms on a cooker circuit but if i disconnect the cooker switch and link the cable straight to the cable going to the cooker connection unit (no cooker connect) i get >500Mohms. so is it ok that the switch lowers my reading?
BTW this is a new circuit. Also on the ring finals the tester goes from 350ish to >500... whats that all about?

Next question...

I have a metal CU and SWA going to an outbuilding with a metal CU but i'm going to TT the building. Which means there will be a parallel earth i guess this is perfectly acceptable?

Thanks in advance
 
How long did you apply the IR test for?

As for the second part, guessing isn't really a good way to do an electrical design, try referencing some regulations instead. But if you are going to guess I'd say you should guess again!
 
1. I wouldn't be reading in to it too much 350M ohms is still a very high reading and would be no cause for concern even on a new build. Think about resistors in parallel, that's all it may be.

2. If your TT'ing the sub main then I would consider earthing the armour solely from the TN end where it will be supplied from and then either installing an insulated consumer unit in the outbuilding and not using a fly lead at that end OR glanding in to an adaptable box first and then feeding in to your metal CU from there. How come you are favouring a TT Earth for the outbuilding anyway?
 
Hi all

I'm using a fluke multimeter and when i test insulation resistance i get a reading of about 300Mohms on a cooker circuit but if i disconnect the cooker switch and link the cable straight to the cable going to the cooker connection unit (no cooker connect) i get >500Mohms. so is it ok that the switch lowers my reading?
BTW this is a new circuit. Also on the ring finals the tester goes from 350ish to >500... whats that all about?

Next question...

I have a metal CU and SWA going to an outbuilding with a metal CU but i'm going to TT the building. Which means there will be a parallel earth i guess this is perfectly acceptable?

Thanks in advance


Plenty of older threads on this subject. Have a search.
 
The steel on the SWA i mean... i know you shouldn't connect the CPC conductor at both ends but i've been told by some people to bond at both ends and just one end by others which means it shouldn't matter if the CU is metal or not? i'm just asking for more advice. And the outbuilding is about 70 something meters away. Hope this clears up my question
 
The steel on the SWA i mean... i know you shouldn't connect the CPC conductor at both ends but i've been told by some people to bond at both ends and just one end by others which means it shouldn't matter if the CU is metal or not? i'm just asking for more advice. And the outbuilding is about 70 something meters away. Hope this clears up my question

Maybe get an electrician in if your not sure.
 
When you TT the outbuilding, neither the CPC or the armour should be connected at the outbuilding end.
 
When you TT the outbuilding, neither the CPC or the armour should be connected at the outbuilding end.

ok, i agree with this... but it will be glanded into a metal CU will this matter? or as tomspark93 said, i should connect it into an adatable box?

thanks
 
You can connect into a plastic adaptable box, use an insulating (plastic) gland into the CU, or I have seen the gland made off into a kind of bracket with just the Line and Neutral then taken to the CU.
 
i would gland into the metal CU as its extraneous conductive part, i can't find why you can't, you ask for help and just get mocked, i see why people say don't go on here

Your not being mocked...I just asked a question. I doubt the metal CU is an extraneous conductive part! If you are making it a TT system at the far end then you need to isolate the suppliers earth from this part of the installation.
 
Last edited by a moderator:
I'm getting the impression you shouldn't connect straight into the metal CU, which doesn't tie up with other advice i've been told, i'm trying to do the job correctly and have had a look in the book but couldn't find anything thats why i ask... thanks simon, didn't know those were available
 
I'm getting the impression you shouldn't connect straight into the metal CU, which doesn't tie up with other advice i've been told, i'm trying to do the job correctly and have had a look in the book but couldn't find anything thats why i ask... thanks simon, didn't know those were available

How come you want to make the remote end TT?
 
Your not being mocked...I just asked a question. I doubt the metal CU is an extraneous conductive part! If you are making the it a TT system at the far end then you need to isolate the suppliers earth from this part of the installation.

i meant the steel of the SWA not the metal CU, sorry

and where can i find this in the book please?
 
As its about 70 something metres away and will be cheaper to install 2 core as its 25mm

What is at the far end? Shed, garage, house, etc.

The price difference between 2core and 3core will be about £1 a meter so about £70. You will more than likely recoup this in labour/material if you don't make the far end a TT arrangement.

Is there anything extraneous at the far end?
 
Last edited by a moderator:
542.1.3.3
Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and be insulated from the earthing arrangements of any other installation.
 
What is at the far end? Shed, garage, house, etc.

The price difference between 2core and 3core will be about £1 a meter so about £70. You will more than likely recoup this in labour/material if you don't make the far end a TT arrangement.

Is there anything extraneous at the far end?

Its a big storage shed with steel structure
 
If you go down the route of making the far end TT, the glands Simon linked to are good or gland in to a plastic dappy box.
 
If you go down the route of making the far end TT, the glands Simon linked to are good or gland in to a plastic dappy box.

ok, thanks for your help, i am trying to do the job properly, i don't know everything and when i don't i try and find out, and asking someone is sometimes easier, as i couldn't find anything in the book, and i've been told to do it incorrectly by other electricians
 
ok, thanks for your help, i am trying to do the job properly, i don't know everything and when i don't i try and find out, and asking someone is sometimes easier, as i couldn't find anything in the book, and i've been told to do it incorrectly by other electricians

The armour or any protective conductor in the cable must not be connected to and must not be simultaneously-accessible with any exposed-conductive-parts in the outbuilding if the outbuilding is being made TT.
 
by far the better method is to use 3 core SWA. it's 25mm, so the 3rd core is more than adequate for bonding, even if it's PME. the extra cost in using 3 core is outweighed by the fact that you won,t need to install earth rods to end up with a pitiful 10 ohm or greater Ra.

and without getting my brain in gear after ale, i'm sure 16mm would give a within limits VD. ( going by your 20A and 70m. about 6V off top of head)
 
Last edited:
by far the better method is to use 3 core SWA. it's 25mm, so the 3rd core is more than adequate for bonding, even if it's PME. the extra cost in using 3 core is outweighed by the fact that you won,t need to install earth rods to end up with a pitiful 10 ohm or greater Ra.

and without getting my brain in gear after ale, i'm sure 16mm would give a within limits VD. ( going by your 20A and 70m. about 6V off top of head)

thankyou, advice taken, and its for solar PV so only have 1%
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
2 Questions
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
37

Thread Tags

Tags Tags
questions

Advert

Thread statistics

Created
iamgary25,
Last reply from
iamgary25,
Replies
37
Views
3,715

Advert

Back
Top