Am wanting to put in a garage CU to divide up garden and garage lighting and power circuits. Currently power comes off kitchen ring that is already protected with a 30mA RCD. For sake of convienience to client, if mower trips RCD they can flick RCD back on at garage RCD rather than having to move furniture to get to main CU and also effecting kitchen appliaces. Has anyone had problems with problem tripping or test results being wrong. Or am I good to go down this route.

Thanks people.
 
Hi.

I be looking at a 50A MCB max for the 10mm SWA.

In free air the max CCC for a PVC SWA without applying any correction factors is 60A.

XLPE SWA does have a higher rating but not by much as it's rated to 90 degrees whereas PVC SWA is rated at 70 degrees.
 
Last edited by a moderator:
The customer has now informed me that the workshop is actually going to be a separate building!

The workshop will just have a ring and lights so quite straight forward.

Can I take the supply from the house to the extension containing the shower, lights and ring, and then take another sub main from there to the workshop?

Or, take 2 SWA cables out to the two locations from small CU at intake with separate MCBs and earth both separately?

Thanks
Harry
 
You could do it eiher way, Harry. You don`t mention distance from 1st outbuilding to workshop - if close then may be better to submain workshop from 1st D/B.

If using seperate submains for each then obviously TT each seperately as discussed.
10mm or > earthing conductor, & 6mm or > for MEB when TT`ing

As you thought, earth SWA at supply end only - insulate at individual D/B`s (as per 542.1.8)

If you do feed a sub from the 1st D/B then you really ought to consider upping to 16mm. As Lenny intimated, even XLPE would only give you 58a if buried, so you`d have to drop down to a 50a breaker. That`s too low IMHO to class as a well designed install with all the loading possible. A 16mm XLPE submain would offer more than enough to allow that 63a as you`d first planned.

Hope it`s useful
 

Reply to 2 RCDs same circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top