HorridToe

I'm thinking of having a new fuseboard fitted. The existing one has 8 fuse in it and is boxed in. The 2 electricians who have come to quotesay i need a board with A main switch 2 Rcds and 8 circuit breakers. the board will not fit in the boxing. My friend has a board with 1Rcd and eight circuit breakers. could i have one of those fitted?
Thanks
 
Having just one RCD is a non conforming and poor way of doing it, the reason for 2 RCD's is so you dont lose all power due to one fault.

Like Lee says a new unit comprised of RCBO's (combination circuit breakers) instead of "standard" circuit breakers provides a solution as you now need no seperate RCD's, did neither of the "electricians" suggest this?

I know I'm unusual but I try to upsell RCBO's to everyone
 
I think that for size the ''fuseboard'' with main switch and RCBO's is the smallest available in width.You will have to have a look at each of the manufacturers dimentions and see if you can't get one to allow spare ways for future additions. although could be slightly more expensive using RCBO's is the best way as under fault conditions only one circuit is tripped off.
 
As above You can fit a RCBO board which means every circuit is on its own individual RCD. Its more expensive than a Dual RCD board but the boards are smaller so will probably fit into the space. The electricians should have discussed this option with you. I normally advise installing a RCBO board as this minimises disruption if there is a fault. Just that one circuit is disrupted rather than loosing half the house.

I Cover Glasgow so get in touch if you want me to come out and provide a quotation.
 
Thanks for the replies. I tol the electrician I was trying to keep the cost down so maybe thats why he didnt mention the Rcbo option. I will ring him in the morning for a price cos if it fits I will prob be cheaper than rebuilding the boxing .
 

Reply to 2 Rcd's? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
352
sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
953

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top