C
Crosswire
230v one side, 24v other side .
Yes or no?
Please quote reg
Yes or no?
Please quote reg
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 2 voltage bands, 1 double pole switch. Yes or No? in the Australia area at ElectriciansForums.net
But if the 12v is run in normal twin and earth (i.e. insulated to 230v) then it is acceptable. Yes?
NO!!.....
There is no way that a DP switch can have 2 different voltages on it from 2 different systems. That's just asking for trouble, pure lunacy!!!
Its for a bathroom light which brings on a fan as well . Not my design, comes from the architect/electrical engineer, who have insisted on a low voltage fan.
This switch would need so many different warning stickers on it, this Architect will probably end up having a heart attack. lol!!!
Hi crosswire,
Presumably your Extra Low Voltage fan is supplied from a SELV source ?
In which case can you not supply the ELV primary source (the 230V AC incoming supply) from the DP switch, as this will then sort all of your problems wrt mixed supplies ?
Just a thought
Edit, or better still from a DP SW FCU suitably fused down (@ 3A)
A question, .... Where are the neutral/return conductors for these 2 systems?? Have they been brought to this switch back box too??
This switch would need so many different warning stickers on it, this Architect will probably end up having a heart attack. lol!!!