2 x 6 mm as main bonding ? | Page 2 | on ElectriciansForums
Discuss 2 x 6 mm as main bonding ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes, you are right, if changing from fuses to RCD protection, then, yes, you are making things a lot safer, but it is still a departure from the Regs, which should not be encouraged unless there is very good reason.
Adiabatic?
Then I cannot see how you can use it for protective bonding conductors.
543.1.1 says this: "every protective conductor, other than a protective bonding conductor, shall be (I) calcualted...... The protective bonding conductor shall comply with 544."
544 then says that a minimum 10mm CSA for PME installations, in table 54.8.
Reply to 2 x 6 mm as main bonding ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
sounds like one of those jobs to swerve and let it be someone else's problem
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...