Looks like this is an overload and negligence by the user whoever that maybe. You would have to test the circuit and then determine whether it's the socket or a wiring issue and then code accordingly.
 
If the sockets are replaced than the test is carried out. There is no reason to put this in the certificate as any C code
Really ...the test is what is found .Then any issues get sorted/new sockets etc .The whole purpose of the test was to clarify a complaint that the first EICR never noted them as been an issues .
 
And the second guy wont class them as a C2 when he found them on arrival still in use .

yep..Interesting that its normally the Other pin . so could be some form of appliance issue etc etc . BUT thats nothing to do with the report ! Its not what was used its the condition of the circuits and fittings etc.
 
Really ...the test is what is found .Then any issues get sorted/new sockets etc .The whole purpose of the test was to clarify a complaint that the first EICR never noted them as been an issues .
Not sure where you're getting your information from. If the socket is replaced and than a full test has been done. Why would you code it?
 
Not sure where you're getting your information from. If the socket is replaced and than a full test has been done. Why would you code it?
Report is what was found Not what was left . The purpose of the test was made clear to them' "Code as you find " . Not Code after completion .Otherwise whats the point of the Test ???

Observations are things which are wrong with your installation that need rectifying and they are coded based on their risk level.​

Fixed Wire Testing ensures your electrical installations are safe and it is governed by the IET Wiring Regulations, the latest version of which is the 18th Edition also referred to as BS 7671 (which came into affect on 1 January 2019).

After completing the fixed wire testing of your installations, your specialist electrical contractor will supply you with an Electrical Installation Condition Report (EICR). This report will indicate any problems or ‘observations’ which are coded according to their risk factor, but what do these codes mean?

Need Fixed Wire Testing?Speak to the team

Observations are recorded on your Fixed Wiring Report, also known as as an Electrical Installation Condition Report (EICR). They are things which are wrong with your installation that need rectifying and they are coded according to their danger level, using the codes C1, C2, C3 and FI.

Code C1​

A Code 1 (C1) observation means ‘ Danger present. Risk of injury. Immediate remedial action required.’

A C1 represents an immediate threat to the safety of your employees, customers or guests and should be rectified or made safe as soon as possible.

An example of a C1 defect would be accessible live conductors due to damage, poorly modified enclosures or removed maintenance panels. Incorrect polarity would also attract a code C1 as it may allow conductive parts, not normally expected to be live, to become live.

Once a C1 threat is identified, your Intersafe engineer will inform the duty holder or responsible person for the installation immediately, both verbally and in writing, of the risk of injury that exists. Access to the faulty circuit may even be blocked, or the circuit turned off until the the defect is fixed.

Code C2​

A Code 2 (C2) is not as severe as a C1, but is still a potentially dangerous defect. They may not pose an immediate threat but are likely to become a danger in the future. A C2 is described as ‘Potentially dangerous – urgent remedial action required.’

The phrase “potentially dangerous”, in the C2 code is designed to point towards a risk of injury from contact with live parts after a sequence of events. A sequence of events could mean that an individual may gain access to live parts through a day to day task that would not usually be expected to give access to live parts.

Code FI​

 
Report is what was found Not what was left . The purpose of the test was made clear to them' "Code as you find " . Not Code after completion .Otherwise whats the point of the Test ???

Observations are things which are wrong with your installation that need rectifying and they are coded based on their risk level.​

Fixed Wire Testing ensures your electrical installations are safe and it is governed by the IET Wiring Regulations, the latest version of which is the 18th Edition also referred to as BS 7671 (which came into affect on 1 January 2019).

After completing the fixed wire testing of your installations, your specialist electrical contractor will supply you with an Electrical Installation Condition Report (EICR). This report will indicate any problems or ‘observations’ which are coded according to their risk factor, but what do these codes mean?

Need Fixed Wire Testing?Speak to the team

Observations are recorded on your Fixed Wiring Report, also known as as an Electrical Installation Condition Report (EICR). They are things which are wrong with your installation that need rectifying and they are coded according to their danger level, using the codes C1, C2, C3 and FI.

Code C1​

A Code 1 (C1) observation means ‘ Danger present. Risk of injury. Immediate remedial action required.’

A C1 represents an immediate threat to the safety of your employees, customers or guests and should be rectified or made safe as soon as possible.

An example of a C1 defect would be accessible live conductors due to damage, poorly modified enclosures or removed maintenance panels. Incorrect polarity would also attract a code C1 as it may allow conductive parts, not normally expected to be live, to become live.

Once a C1 threat is identified, your Intersafe engineer will inform the duty holder or responsible person for the installation immediately, both verbally and in writing, of the risk of injury that exists. Access to the faulty circuit may even be blocked, or the circuit turned off until the the defect is fixed.

Code C2​

A Code 2 (C2) is not as severe as a C1, but is still a potentially dangerous defect. They may not pose an immediate threat but are likely to become a danger in the future. A C2 is described as ‘Potentially dangerous – urgent remedial action required.’

The phrase “potentially dangerous”, in the C2 code is designed to point towards a risk of injury from contact with live parts after a sequence of events. A sequence of events could mean that an individual may gain access to live parts through a day to day task that would not usually be expected to give access to live parts.

Code FI​

Who is requesting
Report is what was found Not what was left . The purpose of the test was made clear to them' "Code as you find " . Not Code after completion .Otherwise whats the point of the Test ???

Observations are things which are wrong with your installation that need rectifying and they are coded based on their risk level.​

Fixed Wire Testing ensures your electrical installations are safe and it is governed by the IET Wiring Regulations, the latest version of which is the 18th Edition also referred to as BS 7671 (which came into affect on 1 January 2019).

After completing the fixed wire testing of your installations, your specialist electrical contractor will supply you with an Electrical Installation Condition Report (EICR). This report will indicate any problems or ‘observations’ which are coded according to their risk factor, but what do these codes mean?

Need Fixed Wire Testing?Speak to the team

Observations are recorded on your Fixed Wiring Report, also known as as an Electrical Installation Condition Report (EICR). They are things which are wrong with your installation that need rectifying and they are coded according to their danger level, using the codes C1, C2, C3 and FI.

Code C1​

A Code 1 (C1) observation means ‘ Danger present. Risk of injury. Immediate remedial action required.’

A C1 represents an immediate threat to the safety of your employees, customers or guests and should be rectified or made safe as soon as possible.

An example of a C1 defect would be accessible live conductors due to damage, poorly modified enclosures or removed maintenance panels. Incorrect polarity would also attract a code C1 as it may allow conductive parts, not normally expected to be live, to become live.

Once a C1 threat is identified, your Intersafe engineer will inform the duty holder or responsible person for the installation immediately, both verbally and in writing, of the risk of injury that exists. Access to the faulty circuit may even be blocked, or the circuit turned off until the the defect is fixed.

Code C2​

A Code 2 (C2) is not as severe as a C1, but is still a potentially dangerous defect. They may not pose an immediate threat but are likely to become a danger in the future. A C2 is described as ‘Potentially dangerous – urgent remedial action required.’

The phrase “potentially dangerous”, in the C2 code is designed to point towards a risk of injury from contact with live parts after a sequence of events. A sequence of events could mean that an individual may gain access to live parts through a day to day task that would not usually be expected to give access to live parts.

Code FI​

The only person giving instructions is the person paying the invoice. Most people will get these jobs done on the 1st visit to save money. Why would you prolonged such a small job I just don't understand?
 
Who is requesting

The only person giving instructions is the person paying the invoice. Most people will get these jobs done on the 1st visit to save money. Why would you prolonged such a small job I just don't understand?

He's asking opinions on what particular code people would give it. There has been a report done where a code wasn't given.

The only question here is what code would people give. Not 'would you change it?'.

Unless I've misunderstood.
 
He's asking opinions on what particular code people would give it. There has been a report done where a code wasn't given.

The only question here is what code would people give. Not 'would you change it?'.

Unless I've misunderstood.
A socket that is not connected I wouldn't give it a code it.🤣🤣
 
A socket that is not connected I wouldn't give it a code it.🤣🤣
Ok...Council demanded landlord gets second EICR . First one "drive by" less than 20 mins no use of a MFT etc etc .Tenant get Council environmental health involved . They turn up .....Try reading the whole post ! Its a report of "Condition as found " Then codes get issued , customer say fix as required , Then Clean bill of health given
 

Reply to 2 x sockets : EICR . What would you code . Then another question ! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
578
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
764
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top