Here's one for the books!!
Got a call from a customer saying were are receiving mild electric shocks from a wall?? So i thinks thats an interesting one i'll go my self and have a look.
Turns up, she shows me to the kitchen were there is an arch way between the kitchen and dining room, shes says its the corners my 2 year you walks past tocuchs the corner and crys, took them two mounths to work out why???
So i get my volt pen out and the whole wall show a voltage present, switch to voltage indicators after doing a quick loop test from a local socket, from the socket screw to the plaster beed is 240V!! no wonder the poor kids been crying.
Flick off a few breakers and find it to be the downstairs lights that's causing the fault, i assume its a nail through the switch wire in the dining room so got to the ceiling rose to disconnect it a find only one cable meaning a junction upstairs.
Procced to upstairs to find laminate floor, luckly its not been fitted very well and not glued together so manage to pull a bit up, pull back the underlay and expose a floor board, start unscrewing it and, ****sssss water hits the ceiling, whip the board out and my mate stick both his thumbs over the two screw hole in both the flow and return, i act quickly get the water turned off and the CH drained down quicker than a plumber on steroids, luckily had the plumbing bits on the van so soldered a couple of new bits of pipe in, What a night mere.
Any way found the fault, was a nail through the switch wire into the meshing of the archway, apparently the mcb was tripping out but they keeped resetting it until it stayed on, it just blew the earth away!! and left all the plaster beed completely live at 240v potential.
What a day
AJ
Got a call from a customer saying were are receiving mild electric shocks from a wall?? So i thinks thats an interesting one i'll go my self and have a look.
Turns up, she shows me to the kitchen were there is an arch way between the kitchen and dining room, shes says its the corners my 2 year you walks past tocuchs the corner and crys, took them two mounths to work out why???
So i get my volt pen out and the whole wall show a voltage present, switch to voltage indicators after doing a quick loop test from a local socket, from the socket screw to the plaster beed is 240V!! no wonder the poor kids been crying.
Flick off a few breakers and find it to be the downstairs lights that's causing the fault, i assume its a nail through the switch wire in the dining room so got to the ceiling rose to disconnect it a find only one cable meaning a junction upstairs.
Procced to upstairs to find laminate floor, luckly its not been fitted very well and not glued together so manage to pull a bit up, pull back the underlay and expose a floor board, start unscrewing it and, ****sssss water hits the ceiling, whip the board out and my mate stick both his thumbs over the two screw hole in both the flow and return, i act quickly get the water turned off and the CH drained down quicker than a plumber on steroids, luckily had the plumbing bits on the van so soldered a couple of new bits of pipe in, What a night mere.
Any way found the fault, was a nail through the switch wire into the meshing of the archway, apparently the mcb was tripping out but they keeped resetting it until it stayed on, it just blew the earth away!! and left all the plaster beed completely live at 240v potential.
What a day