Hello,
Just wanted to share a fault I had today and was wondering if anyone else has come across it. So I wired a kitchen and the customer supplied the faceplates (I know...)
So after a lot more time explaining what they needed to buy and that a light switch would not work as an isolation switch for the oven(even tho they claimed that is how the electrician who wired their old house done it!)
Anyway, they called me back saying that the oven and dishwasher were tripping the RCD. I found that the 20a double pole gird switches must be switching the live before the neutral and because the new oven they bought have electronics in them this current must be wanted to return on the cpc and causing the RCD to trip.
The gridswitches were Varilight, which i would not have picked myself but they had already bought the other faceplates from this brand. I did not think they were a bad brand and I am fairly surprised with this fault and was wondering if it was more common than i realise.
 
Not one I've run into, though I don't install grid switches that often - and they usually don't get switched off very often. Is it repeatable - as in tripping every time the switch is turned on, and doesn't happen if the rcd is reset with switch on?

Varilight are a fairly decent brand - did they source them from a reputable supplier, or just buy them on ebay?
 
Hi,have you done all appropriate tests,to ensure this fault is the switch?

You would not want to obtain the best double pole switch in the world,only to find out there are other issues.

How are the grid switches configured,for these two machines?

...I bet it's easier to reset the RCD,than the clocks ...
 
All initial inspection was done at when the kitchen was wired. Today I rechecked polarity, earth loop, rcd ramp, rcd times, the end to end on the ring, resistance L-N (shorted at board) to each outlet.
The set up is kitchen ring with socket outlets 7 appliances on a 20amp switch each to a single socket. The fridge, freezer, cooker hood and wine chiller all work, but are very basic appliances, the oven, microwave and dishwasher are the ones causing the problem.
You would be able to switch on the grid switches maybe 1 in 3 times and not trip the RCD but if they are all on the RCD will reset. I have bypassed the neutral on the switch just now and it all works fine now, i could not get the rcd to trip when i turned the items on and off repeatedly
 

Reply to 20 amp double pole switches in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top