Done a few EICR's recently and having a blonde moment regarding storage heaters.
All storage heaters in the property are rated at 1.5kw and fed by 1.5mm HR flex, circuits are individually fed in 2.5mm T&E by individual 16A MCB's.
All perfectly normal, except that each one is isolated locally by a 20A DP. I'm sure in the past I've been told by "old timers" that any appliance less than 3kw should be isolated by an FCU, or am I thinking of something else? I get the whole discrimination thing, but is there actually anything wrong with the way this installation is done? ie replace all DP's with FCU's? What's the thought on fault codes for this? I don't think there's a problem as the flex can handle over 16A (clipped direct) but I keep hearing the old timers voice, so maybe a few more voices might drown it out!
All storage heaters in the property are rated at 1.5kw and fed by 1.5mm HR flex, circuits are individually fed in 2.5mm T&E by individual 16A MCB's.
All perfectly normal, except that each one is isolated locally by a 20A DP. I'm sure in the past I've been told by "old timers" that any appliance less than 3kw should be isolated by an FCU, or am I thinking of something else? I get the whole discrimination thing, but is there actually anything wrong with the way this installation is done? ie replace all DP's with FCU's? What's the thought on fault codes for this? I don't think there's a problem as the flex can handle over 16A (clipped direct) but I keep hearing the old timers voice, so maybe a few more voices might drown it out!