Interesting, what's your regs there then?
I'm assuming the area of the waste disposal would be considered Zone 1 under SANS regs
7.1.4.3.1 In zones 0, 1 and 2, no switchgear and accessories shall be
installed except that emergency push buttons, which operate at a safety
extra low voltage at nominal voltage not exceeding 12 V, are permitted in
zones 1 and 2.
7.2.4.2.4 In a circuit in zone 0 or zone 1, there shall be
a) one appliance only,
b) no junction boxes for voltages exceeding 12 V, and
c) only conduits of insulating material.
7.2.4.3 Switchgear and accessories
7.2.4.3.1 There shall be no switchgear or accessories in zones 0 and 1.
7.2.4.3.2 In zone 2, any socket-outlet or switch shall be
a) supplied individually by a class II isolating transformer that is installed
outside the zone and that operates at a nominal voltage not exceeding
50 V, or
b) protected by an earth leakage protection device that has a rated earth
leakage tripping current (rated residual current) IΔn not exceeding
30 mA. Amdt 3