Is a 20A 2.5mm radial sufficient for 2 sockets in a utility room? Will be a tumble dryer/washing machine plugged in and a spare socket used for a Hoover occasionally.
Sure, 2G is rated 20A with potential of 26A. The cct is already in place, just wondering my best method as customer wants to change the existing room to a utility and plug in washing machine and tumble dryer. Was thinking run a 2.5mm back to the consumer unit and make it a 32A ring. But thought it was a bit excessive for 2 double sockets?
Typical ratings for washing m/c 2.2kW, tumble dryer 2.5kW, an old vacuum anything from 900W to 2kW!
You're around 20A with just the washing m/c and dryer, let alone plugging anything else in.
I don't thing the rfc idea is at all excessive in this case! Could always add another socket 🤪
If you are going to put in a return leg for the existing socket, why not put in a new radial instead, as too the Vacuum cleaner will it really be used at the same time as both the others?
The return leg can be installed in some surface trunking in the corner back to consumer unit to save chasing. A vacuum might not even be plugged in, just thinking worst case loading. Likely the other socket will remain unused.
Reply to 20A radial 2 double sockets in the UK Electrical Forum area at ElectriciansForums.net
Thanks, that seem a better option. Thought I'd ask the question before asking for a installation quote.
Why aren't you asking them?