Been having a debate with a mate this afternoon about a circuit in his house.
The circuit is a radial with 16 amp mcb that was previously used to feed his immersion heater that was removed when a boiler was fitted- he doesn't have a radiator in the conservatory and cant afford one to be fitted. he is going to divert the cable from his kitchen where the Cu is out the wall into the conservatory. Then get the electricians at his work to give it the once over.
He is of the view the way to wire a 3kw electric wall mounted heater in is to use a 13 amp FCU. I am saying no, have to use a DP 20 amp switch fed from breaker. 3kw is just over 13 amp 3000/230 = 13.04 amps and given the circuit is a radial fed with a 16 amp breaker with nothing else on it, the fcu is doing nothing of use and is un-necessary. Also adding 3kw heaters onto a ring will likely overload it.
This is the bit that then made me chuckle, he has recently been on a job - hes a surveyor for social housing outfit where the electricians have put 2 separate 3kw heaters on 13 amp fcu's joined to the rfc during refurbishments of some social housing units. He seemed oblivious to the issue of having a couple of 3kw heaters plus the other household appliances on the one 32 amp ring!
It makes you wonder how there haven't been more grenfell fires if the supposed people in charge of quality and standards sign off things like this. Of course given the low power draw of a lot of modern stuff its possible that the circuit might take the 2 heaters in the social housing example, but you don't know if the tenant will plug hoovers, irons and god knows what else in when the heating is on max.
 
Dub pole switch, maybe an fcu 30 yrs ago when they could actually cope with 13A but not the tat you get now.
I think some of the better quality fcus would hold a good load but i have seen far too many cheap accessories that seem to have ever thinning pieces of metal in them, You also dont know anymore where a lot of the stuff is made as people cash in on the names and make crap stuff.
 
If the heater came with a 3 pin plug, I'd use it. If no plug, then I'm not a fan of 3kW loads in FCU either. And just be be a complete Abacus, the 3kW heater will likely be rated that at 240V :) .
 

Reply to 20amp DP switch or fcu for 3kw heater? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

  • Question
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
Replies
2
Views
480
loz2754
L
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top