I saw an oven that was rated at 3,100 watts. Now most would say that cannot be fitted on final ring circuit as rule of thumb. But:
3,100 watts draws amps of:
14.09 amps @ 220v
13.47 amps @ 230v
12.91 amps @ 240v
12.4 amps @ 250v

If the installation is 240v or 250v then it safely inside the 13 amp of a final ring circuit.

The question is, and the regs aficionados can help here, what is the voltage that should be used to assess, as maybe the voltage will vary in an installation over the years.
 
I think a lot of the problem is some of the cheap plugs that are around these days. Bring back the old MK ones with proper knurled terminal screws with built in washers. Lovely!
As a young apprentice with the local Health Authority I fitted dozens of these, lovely plugs and it brings back memories. Nobody ever questioned why my gran's twin tub had 'Hospital Property' embossed on the lid of the plug,or should that be plug top. ?
 
Had a lady two weeks ago with gas hob and electric oven all controlled with normal cooker point, she wanted to change the hob to electric, no problem, she buys new Bosch induction hob, and I go there with a click dual outlet cooker outlet and some 4.0mm flex to connect it all up.
When we take it out of the box it is rated at 3700 watts and is factory fitted with a lead and 13 amp plug so as we are told to follow manufacturers instructions I then duly fitted a single socket to the cooker outlet circuit and plugged the Hob in.
Did not seem the right thing to do but to date have had no call backs, I do have to go there to do some other work shortly and will check it out and see how it is performing.
This is playing on my mind as the appliance is capable of drawing over 13 amps. If the appliance came with no 13A plug, an electrician would not fit one on this appliance, as it is capable of drawing over 13 amps. Or fit it on a final ring circuit. It is obvious the makers have taken diversity into account, as the load is split between four current drawers, the rings, which will be cutting in and out via thermostats.

This makes me think that the combination oven (microwave and oven in one) example I mentioned at the beginning of this thread at 3,100 watts is suitable for 13A plug and final ring circuit. The instructions do not mention anything about amperage, I posted them, only that a DP isolator needs to be fitted. A 13A sockets have DP isolation. A spur off a ring with 20A DP isolator switch, or a 13A FCU, feeding a 13A socket behind the oven would conform to that.

Yes, I know it is best the oven has its own dedicated supply to be sure, that is not the point. Many would like to fit an oven like this, marginally over the 13 amp cut off point, as it would save ripping a finished kitchen to pieces.
 
Last edited:
Had a lady two weeks ago with gas hob and electric oven all controlled with normal cooker point, she wanted to change the hob to electric, no problem, she buys new Bosch induction hob, and I go there with a click dual outlet cooker outlet and some 4.0mm flex to connect it all up.
When we take it out of the box it is rated at 3700 watts and is factory fitted with a lead and 13 amp plug so as we are told to follow manufacturers instructions I then duly fitted a single socket to the cooker outlet circuit and plugged the Hob in.
Did not seem the right thing to do but to date have had no call backs, I do have to go there to do some other work shortly and will check it out and see how it is performing.
How many rings did that hob have?
 
When we take it out of the box it is rated at 3700 watts and is factory fitted with a lead and 13 amp plug so as we are told to follow manufacturers instructions I then duly fitted a single socket to the cooker outlet circuit and plugged the Hob in.

3700W requires a 16A supply. The hob probably has internal power management setttings to allow the total load to be limited to 16, 13 or 10A which should be set during commissioning. The rating given on the box is 3700W because that is what the hob is physically capable of delivering.

If you scroll down to the 'installation' tab on this link, Bosch have shown the 3700W limit as corresponding to the 13A plug version. I suspect that is a copy-and-paste mistake from the 16A Schuko-plug version and that they do not intend a 13A plug to supply 3700W.

 
3700W requires a 16A supply. The hob probably has internal power management setttings to allow the total load to be limited to 16, 13 or 10A which should be set during commissioning. The rating given on the box is 3700W because that is what the hob is physically capable of delivering.

If you scroll down to the 'installation' tab on this link, Bosch have shown the 3700W limit as corresponding to the 13A plug version. I suspect that is a copy-and-paste mistake from the 16A Schuko-plug version and that they do not intend a 13A plug to supply 3700W.

It says:

This hob is equipped with a UK 3 pin plug for an easy plug & play installation. The plug limits the maximum power output to 3.7 KW. For higher power output, please select a hob without plug and ensure installation is carried out by a qualified electrician

The 13A UK plug limits the maximum to below 3.7 kW - I think a mistake here in the writing.
 
It says:

This hob is equipped with a UK 3 pin plug for an easy plug & play installation. The plug limits the maximum power output to 3.7 KW. For higher power output, please select a hob without plug and ensure installation is carried out by a qualified electrician

The 13A UK plug limits the maximum to below 3.7 kW - I think a mistake here in the writing.

Agree, it seems like badly worded English.
 
The 13A UK plug limits the maximum to below 3.7 kW - I think a mistake here in the writing.
Indeed, as I pointed out in post #59.

NEFF T36FB41X0G
BOSCH PUE611BF1B
SIEMENS EU631BEF1B

All four ring 13A induction hobs.

Bosch, Neff and Siemens are different brands of the same company, so I would expect to find those three hobs to be internally the same core product.
 
[ElectriciansForums.net] 220v. 230v, 240v, 250v?
My Smeg can be single or three phase.
 
It says:

This hob is equipped with a UK 3 pin plug for an easy plug & play installation. The plug limits the maximum power output to 3.7 KW.

Interesting comment from the manufacturer, bearing in mind the 13amp fuse is installed primarily to protect the CABLE supplying the hob.

The 13A UK plug limits the maximum to below 3.7 kW - I think a mistake here in the writing.
13amp plug limit maximum? Unlikely. A 13 amp plug may well carry a few amps above its rating for a significant period
 
Interesting comment from the manufacturer, bearing in mind the 13amp fuse is installed primarily to protect the CABLE supplying the hob.


13amp plug limit maximum? Unlikely. A 13 amp plug may well carry a few amps above its rating for a significant period
Yes, fuses blow at above 13A, and only when sustained over-current is being drawn. It is a bad design that relies on the fuse not blowing.
 
Had a lady two weeks ago with gas hob and electric oven all controlled with normal cooker point, she wanted to change the hob to electric, no problem, she buys new Bosch induction hob, and I go there with a click dual outlet cooker outlet and some 4.0mm flex to connect it all up.
When we take it out of the box it is rated at 3700 watts and is factory fitted with a lead and 13 amp plug so as we are told to follow manufacturers instructions I then duly fitted a single socket to the cooker outlet circuit and plugged the Hob in.
Did not seem the right thing to do but to date have had no call backs, I do have to go there to do some other work shortly and will check it out and see how it is performing.
Was this to a cooker radial 6mm cable? On on a final ring circuit? If on cooker radial, the plug could have been removed with the hob set to 3.7 kW drawing 16A.
 
Interesting comment from the manufacturer,
But I think we have a concensus that this is a mistake.

Agree, it seems like badly worded English.
Achtung!
The Kookerhob is greatpowerneeding and the elektrische Kabels have to be placed bei the Skilledtechnician. In Europe is to make 16A Kuppling with a Schukostecker allowed. In Grossbritannien, because the dumme Plugtoppen the Weakcontacts and Stupidlittlefuses which like Heatelements often the Outburning or Downmelting are the cause of are required to have, is max. 13A permitted. Offchoppen von Plugtoppen is ABSOLUT NICHT GESTATTET!
 
But I think we have a concensus that this is a mistake.


Achtung!
The Kookerhob is greatpowerneeding and the elektrische Kabels have to be placed bei the Skilledtechnician. In Europe is to make 16A Kuppling with a Schukostecker allowed. In Grossbritannien, because the dumme Plugtoppen the Weakcontacts and Stupidlittlefuses which like Heatelements often the Outburning or Downmelting are the cause of are required to have, is max. 13A permitted. Offchoppen von Plugtoppen is ABSOLUT NICHT GESTATTET!
Thanks, Buzz... that makes perfect sense...


Oh.. it wasn't Buzz??
 
But I think we have a concensus that this is a mistake.


Achtung!
The Kookerhob is greatpowerneeding and the elektrische Kabels have to be placed bei the Skilledtechnician. In Europe is to make 16A Kuppling with a Schukostecker allowed. In Grossbritannien, because the dumme Plugtoppen the Weakcontacts and Stupidlittlefuses which like Heatelements often the Outburning or Downmelting are the cause of are required to have, is max. 13A permitted. Offchoppen von Plugtoppen is ABSOLUT NICHT GESTATTET!
in myold house, back in the 70's the fuse box ( wylex with 3036's) was labelled "Achtung. Gerfingerpoken Verboten".
 

Reply to 220v. 230v, 240v, 250v? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

@pc1966 hits the nail on the head. Electrically, there is no difference in the demand placed on the cables, whether the load is one 20A appliance...
Replies
8
Views
3K
S
Working in the Jewish community can be an interesting time, but they're normally good people to work for. Would defo install more than 1 Ring though.
Replies
8
Views
7K
Specialist
S
B
  • Question
.....Right.....firstly,the obvious. You have not only left it quite late,to design and fit the desired equipment,you have also left it last. Some...
Replies
3
Views
3K
ELECSA Certification Scheme Regulations Clarification (ELECSA Assesment)
Good start hope the rest is plain sailing also.
Replies
73
Views
10K
P
You tell us? You've not really mentioned it.
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks