Standard 230 v hairdryers wired into rcbo protected spurs poolside, id say zone 2 but didnt measure. Hair dryer cable is 2 core, the cable had been damaged leaving the neutral snapped and exposed at the hairdryer end, floating neutral... Someone apparently grabbed the cable and received a shock. With no path to earth what would it take for the rcbo to operate. Maybe if the floor was wet enough to find a path etc. Iv recommened a hand dryer designed for the application be installed.
 
The RCBO will operate either as a result of overload or more than 30mA leakage (leakage being the difference between the current flowing in the line and neutral) no matter how that leakage originates.

Theoretically if someone grabbed it and got a shock, they have completed a line/floating neutral to earth circuit and I would have expected the RCBO to trip if they felt it.

A dryer designed for the location is a good start, but maybe consider mechanical protection for the cable as well... PVC conduit perhaps.
 
Conduit wouldnt be practical. Obviously the hair dryer needs to be moveable to dry your hair. Lol... An ip type has no cable just a hose. In terms of the rcbo not operating, i didnt speak to the person who reported. Id say it was a flash when the cable broke and maybe they didnt get a shock. Installation is only 3 years old.
 
What type of site is this?

I cannot for one second believe it would be a site open to the public with that kind of nonsense going on. I'm sorry, but I'd be suggesting to the client they loose the hair driers and put them in a more sensible place (like the changing rooms perhaps), and if they weren't willing to do that, I'd probably walk.

Zone 2 extends to 3.5m from the waters edge, but you're still going to be sopping wet if you walk that far. It's a disaster waiting to happen and I'd say the person this happened to is lucky.

In the case you described, then the RCBO won't trip because there was no overload, no fault current and potentially no leakage.
 
It is a new site. Local council public swimming pool. On the schedule its says 60898 which they must have been on originally. Poor design. Someone has put them on rcbo since but its not sufficient. I have not checked the regs yet but im sure they have to be designed for use or elv on swimming pool. To be fair the client has already been on and put the order in to replace. Theyre not on rcd spurs theyre on rcbos in the db which is in plant room..
 

They look like they might be just the ticket. Decent containment on the cable and they'd probably be a good way to move forward.
 
How often was the existing equipment formally inspected for serviceability?

New kit is all well and good but if processes aren't in place this could happen again.
 

Reply to 230v hair dryer swimming pool. in the Electrical Appliances & Whitegoods Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top