H

hospital

Good evening ladies and gentlemen,has anyone recently taken the 2330 303 written exam,the fault finding and rectification one if so any pointers would be most welcome.

Thankyou,Peter.
 
when working out the Zs ,say you have 0.28 as Ze, R1 +R2 values , say it was a ring circuit in 2.5/1.5mm and was 63 meters long . is this correct 19.51 x 63 / 1000 / 4 = 0.31 + 0.28 = 0.59 as Zs????
 
Upvote 0
when working out the Zs ,say you have 0.28 as Ze, R1 +R2 values , say it was a ring circuit in 2.5/1.5mm and was 63 meters long . is this correct 19.51 x 63 / 1000 / 4 = 0.31 + 0.28 = 0.59 as Zs????

I assume you are doing (r1+r2)/4 end to end resistance values of the line and the CPC of the ring (as opposed to R1+R2 divided by 4) in which case I think it is correct, but I don't have my OSG with me at the mo.
But I believe measured Zs can have a lower value due to parallel paths
 
Last edited by a moderator:
Upvote 0
"the resistance between line and earth is measured at each socket. the readings obtained... will be substantially the same and the value will be approximately one-quarter of the resistance of the line plus cpc loop resistances, (i.e. (r1+r2)/4"
quote from pg82 OSG so I think you are right
 
Upvote 0
i have good idea of ring testing, but im just playing with sums in my head, as i do, as im a pull cord gack... naw but if you were working out lengths of circuits before installed..
 
Upvote 0
Just had to do some for my first design job, working out Zs for appropriate protective devices, I'm hoping I got it right because I'm installing it on Tuesday, just had to do Ze and pfc psc tests today. But I am going to be triple checking my calculations and relevant regs ;)
 
Upvote 0

Reply to 2330 303 written paper in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
380
  • Question
From the title and first post it is not clear whether you are looking to install surge protection or a lightning protection system (LPS) or is it...
Replies
3
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top