Hopefully it helped. The starting point is that you are going to need the prospective fault current, so either
-they tell you what it is, or
-they tell you the Ze and the R1+R2 which add together to give the Zs and you can calculate the fault current ( 230 / Zs) , or
-if they are making you work very hard they will tell you 'so many' meters of a certain type of cable and you'll have to calculate the R1+R2 and then add it to the Ze, giving you the Zs, and calculate the fault current (230/Zs)
Having got the fault current you need to know how quickly it will trip the protective device from the relevant graph.
 
Upvote 0
Hopefully it helped. The starting point is that you are going to need the prospective fault current, so either
-they tell you what it is, or
-they tell you the Ze and the R1+R2 which add together to give the Zs and you can calculate the fault current ( 230 / Zs) , or
-if they are making you work very hard they will tell you 'so many' meters of a certain type of cable and you'll have to calculate the R1+R2 and then add it to the Ze, giving you the Zs, and calculate the fault current (230/Zs)
Having got the fault current you need to know how quickly it will trip the protective device from the relevant graph.
Hi Tim,

This is really the only info they are giving me I don’t know if I’m just being stupid but I can’t get my head around this.
 

Attachments

  • [ElectriciansForums.net] 2365/615 Question 5 Help please
    C085DD96-A739-472D-8A87-6131E47DD0BA.jpeg
    142.2 KB · Views: 42
Upvote 0
Ok, that's a start. 70 degree PVC singles in conduit and 16 amp protective device.

You are missing:
The length of the circuit - is there a diagram showing the room? Does a previous question address this?
The size of PVC singles (e.g. 1.5 sq mm, 2.5 sq mm. It can't be 1 sq mm as that can't carry 16 amps in conduit on a wall). This affects the resistance, and therefore the fault current.
The specific protective device (though one could assume a B16 MCB)
The earth loop impedance of the origin (Ze). (the resistance back to the supply transformer, which also affects fault current)

Do the previous questions get you to work out this, e.g. select an appropriate cable size for the fridges circuit for reference method B?

To use the adiabatic equation you need to know the actual prospective fault current for the actual circuit and right now you don't appear to have enough information.
I can only assume that other questions you have already answered are related to it too.
 
Upvote 0
Has anyone got the full list of questions for this unit my tutor is away for weeks on end and what to start the assignment early as I like to keep on top of things.
 
Upvote 0
Ok, that's a start. 70 degree PVC singles in conduit and 16 amp protective device.

You are missing:
The length of the circuit - is there a diagram showing the room? Does a previous question address this?
The size of PVC singles (e.g. 1.5 sq mm, 2.5 sq mm. It can't be 1 sq mm as that can't carry 16 amps in conduit on a wall). This affects the resistance, and therefore the fault current.
The specific protective device (though one could assume a B16 MCB)
The earth loop impedance of the origin (Ze). (the resistance back to the supply transformer, which also affects fault current)

Do the previous questions get you to work out this, e.g. select an appropriate cable size for the fridges circuit for reference method B?

To use the adiabatic equation you need to know the actual prospective fault current for the actual circuit and right now you don't appear to have enough information.
I can only assume that other questions you have already answered are related
Hi Tim. Im also doing the same project. the pfc is listed in the photo how would i use it or can you show me what steps i should take for this question.
 

Attachments

  • [ElectriciansForums.net] 2365/615 Question 5 Help please
    IMG_3991.jpg
    1.1 MB · Views: 7
  • [ElectriciansForums.net] 2365/615 Question 5 Help please
    IMG_3992.jpg
    1.8 MB · Views: 7
Upvote 0

Reply to 2365/615 Question 5 Help please in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
If you are using Zdb you do not add on Ze as that is already incorporated into Zdb.
Replies
25
Views
1K
  • Question
Mine was the same off my turor I’ve had to change loads 🤦‍♂️
Replies
2
Views
2K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
526
  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
1K
  • Question
need same help please i would be interested as well
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top