Afternoon Gents, just a query regarding volt drop and extending the equipotential zone on a PME in the level 3 design project.
In my design I used a 16mm armoured and the associated volt drop was 5v, this left 1.9 volts for the lighting ring in the summer house. Tutor said not to worry about the feeds volt drop as it was not cumulative and wouldn't effect the lighting circuit. Is this correct, or just leaving it out for sake of simplicity.
Also, if I were to use a 16mm feed, would that also allow the PME to export its earth? The summer house has sinks and toilets so I assume will have copper piping to underground. I can recall seeing a 10mm bond would mitigate the risk but cannot find the appropriate reg with regards to out-buildings. Would a TT earth stake be a better solution?
Thanks for looking this over and look forward to your inputs!
In my design I used a 16mm armoured and the associated volt drop was 5v, this left 1.9 volts for the lighting ring in the summer house. Tutor said not to worry about the feeds volt drop as it was not cumulative and wouldn't effect the lighting circuit. Is this correct, or just leaving it out for sake of simplicity.
Also, if I were to use a 16mm feed, would that also allow the PME to export its earth? The summer house has sinks and toilets so I assume will have copper piping to underground. I can recall seeing a 10mm bond would mitigate the risk but cannot find the appropriate reg with regards to out-buildings. Would a TT earth stake be a better solution?
Thanks for looking this over and look forward to your inputs!