IS there a minimum distance between the consumer unit and waste pipe. The waste pipe is on the left of consumer unit.
yes - so i need to replace consumer unit. However, does it need to be relocated to meet regs?Is this part of the EICR property from your other thread?
Deleted content due to seeing message above re: keep to original thread. Will reply same if the thread continuesIS there a minimum distance between the consumer unit and waste pipe. The waste pipe is on the left of consumer unit.
you are right, i do not have the EICR report. I have spoken since the the inspection, a number of times to person doing the inspection. He was adament that there needs to be a minimum of 300mm from waste pipe to consumer unit,We can leave the other thread as “electrician hasn’t given me the report” problem and have this one to discuss what’s actually cropped up on the report…
You don’t actually know what’s on it as you haven’t got it…. Was it just the tester saying you needed a new board without explaining why?
The two boards there could possibly be amalgamated into one, bring it over to the right hand side, away from the drain pipe.
Do you know any other faults?
A satisfactory EICR can have C3 coded faults. Simply means improvement recommended.
Unsatisfactory would be C1 - dangerous or C2 - potentially dangerpus.
As the property is a rental, there is also the safety of the tenants to consider.
A C3 may well be ok for the report, but perhaps should be upgraded anyway.
No there is no need for 300 mm distance in BS 7671 . The NHBC Technical document requires 300mm from electrical consumer units and the edges of sink / basins. Building regs require 300mm distance from the edge of sinks / basins in Kitchens to reduce risk of splashes - is that where he is getting the distance from?. I have had this before from builders / electricians but it is not a BS7671 requirement.Deleted content due to seeing message above re: keep to original thread. Will reply same if the thread continues