2391-10 Written Exam - 01/12/11

Wot about the Supply Transformer to MET for tt, tns, tncs? Did u start at Transformer i.e. transformer, supplies Line conductor.. etc, or start at MET i.e. MET, installations Earthing Conductor...?
 
Upvote 0
The volt drop answer was 0.38x30Ax1.2=13.68v. Which is over 11.5v and exceeds the maximum volt drop. But I couldn't work out if the roller shutter was in a private or public installation as it was in a retail outlet but not part of the shop??????! This would change the max volt drop.
 
Upvote 0
Our tutor told us the day before the exam that you no longer multiply by 1.2 now. Hope he was right or I am wrong on that one!
 
Upvote 0
hi marnik have you maid it up because the formula for calculating the volt drop is Vd=(R1+Rn)xId
and on GN-3 said that on circuits supplying motors with high inrush starting current is allowed higher voltage drop and 1.2 factor is not mentioned.
 
Upvote 0
There is different % of allowed voltdrop from a electrical installation that is in a public area than one it is a private area. Hope this solves your ???????????

Sounds like we are all being taught something different!
 
Upvote 0
It's not areas it's distribution networks there are public distribution and private distribution ie if a factory has its own transformer in its own substation or public is if you are off a standard substation
 
Upvote 0
There is different % of allowed voltdrop from a electrical installation that is in a public area than one it is a private area. Hope this solves your ???????????

Sounds like we are all being taught something different!

I suggest you have another think about that.

As far as I was aware the only deviation in the volt drop values allowed in the BS 7671-2008 concerns motors and is regulation 525.4 in the BRB. Now as the C&G 2391 based on the BS 7671 perhaps that is what you mean when referring to a roller shutter.
 
Upvote 0
Q1 was something like this - an inspection of an installationis being done as part of an intial verification. What 3 conditions must be verified?

Q4 purpose of initial verifcation as per GN3
 
Upvote 0
In a way you are both right App 12 has two for a public (DNO) system and two for a private supply. 525.4 is as stated in quote

The question as I remember was something like - a single phase motor is running slow and gets hot and it is believed it is a volt drop issue
1. calc vd if L1 & LN is 0.38 and motor load is 30A
2. does vd above meet regs
3. one course of action to be taken if vd is too high and why

I suggest you have another think about that.

As far as I was aware the only deviation in the volt drop values allowed in the BS 7671-2008 concerns motors and is regulation 525.4 in the BRB. Now as the C&G 2391 based on the BS 7671 perhaps that is what you mean when referring to a roller shutter.
 
Upvote 0

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top