Anyone help with some cable calcs for my designe project, i must be missing something here.
Im trying to work out and show my calculations for cable sizing of a 32A ring
Length is 78 M
Number of 13A double sockets is 7
Ib is 32A
In is 32A RCBO
It should be In / Correction factors of wich i only have a grouping factor of 0.41
This makes it 32/0.41 = 78A
The above formula say that i should be using a cable capable of carrying 78A wich brings it upto 25mm ????????????? (ref meth B,singles) table 4D1A.
I know this is wrong but where am i mucking up.
Please help