List three instrument tests which are undertaken to confirm the correct operation of a
30mA RCD installed to supplementary protection against direct contact.
 
at half the rated value of the device (15mA)
at the rated value (30mA)]
and at 5 times the rated value (150mA)
All on both cylces
at 15mA no trip
at 30mA less than 200mS
at 150mA less than 40mS

(this was done from memory after a couple of beers and match of the day so double check me)
 