sorry guys need to rack your brains again just want to make sure i get the right answer as im goin over my notes


State the two conditions that need to be taken into account when comparing measured Zs value and the maximum values quoted in bs7671



PLEASE HELP IM SOO NERVOUS IM PULLING MY HAIR OUT!!!!!!!


thanks again!
 
I would say,

1, ambient temperature, if the temp is high, this will increase the resistance and so increase maximum measured Zs, if low it will have the opposite effect.
2, The tabulated values in BS7671, these need to be corrected using the 0.8 correction factor to ensure that the measured Ze is acceptable.

That is 2 conditions and 2 reasons, but i am not saying that this is the correct answer.

Cheers.........Howard

PS a bit of tip with the 2391. When asked to show all calculations, show them, even if you get the result wrong you can still pick up points for showing the correct method.

Oh and good luck, lets us know in due course how you get on.
 
When measuring Zs, the conductors will be at the ambient temperature, not at their operating temperature.
An adustment to the measured values must be made to accomodate this difference.
The 80% rule of thumb is applied for operating temperatures of 70°C, and measuring when the ambient temperature is 20°C.
A different percentage will have to be used if the operating temperature is lower than 70°C, or if the ambient temperature when measuring is either higher or lower than 20°C.
GN3 Appendix B, OSG Appendix 2 and BS7671 Appendix 14 have information relating to this.
Another factor to consider is the temperature rise in the conductor operating temperature that will occur when conductors and circuits are bunched together, and those caused by installation methods. These are usually associated with current carrying capacity, but as they will cause temperature rises, should also be considered when assessing conductor operating temperature.
 
My answer would be very similar to that of spinlondon's.
Applying reference to appendix 14 of BS7671 shows a greater understanding than the commonly phrased 'rule of thumb'.
I would maybe also write down an understanding between the effects of a conductors resistivity/conductivity according to ambient and operating temperatures and the reason the two exist.

I'm just setting my class up for the exam now.

Good luck to you.
 

Reply to 2391 exam in 3 hours need help with a question!!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top