a) the effect on earth fault protection provided by a BS EN 60898 circuit breaker if it is connected in the neutral conducter only

b) why the effect in a) above occurs.
 
In affect the neutral conductor is not part of the earth fault loop.

It goes like this

Fault
CPC
Earthing conductor and MET
The return path via earth TT general Mass of earth TNS TNC S Metalic return.
The earth neutral of supply transformer
The transformer winding
The line conductor back to the point of the fault.

So if the protective device was in the neutral conductor the chances are it will not operate.

Hope this makes sense
 
Draw the earth fault path and get it in your head as its 15 easy marks.

Make sure you put the right system on the drawing that your are asked so note TT TNS or TNC-S.

If you are asked for a TNS and put in a ROD for a TT you will be deducted alot of marks.


This question along with testing continuity ring final ccts conductors often comes up.
 
Last edited:
Good luck Kenny and try and remember a couple if questions and post them up to help others (like me) that are studying for it. Keep calm and I'm sure you'll be fine.
 
will do i will try to remeber as many as i can and will try to help others as i have had so much help off here i think i would of be in a lot worse state than i am now.
 
a) the effect on earth fault protection provided by a BS EN 60898 circuit breaker if it is connected in the neutral conducter only

b) why the effect in a) above occurs.
Surely the answer is you have no protection if there is a fault between line and cpc?
The CPC will be the fault path and the current will keep flowing until you pop the main incoming fuse, As there is No protective device in the line conductor.
Thats what id go for mate, I mite be wrong. Hope this helps.
Oh and by the sounds of it, Its a short answer question.
So you d get away with putting A) If the Protective device is connected in the netural conductor if would not operate under fault conditions(line to CPC)
 

Reply to 2391 help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
Correction on checking exchange rate: the EVS 3-user copy is 3.8 times cheaper than the BSI "member's half price" single-user copy.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top