yes mate i was trying to highlight the r1 + r2 part, i got the shock of my life when i read the examiners comments!
Last edited by a moderator:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 2391 Odds and sods in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Referring back to SWA again there is no mention of special IR tests but GN3 page 34 states:
"Installation incorporating SWA will introduce parallel paths to protective conductors.
In such situations the R1+R2 test will need to be done prior to final fixing"
So there you go, there is no mention of special IR test procedures but R1+R2 is specifically mentioned so I guess you would have to remove the CPC from the board to test R1+R2 if the SWA had been already installed and the armour had been earthed.
It would be easier doing this way than trying to remove the armour earthing if you had a metal clad board.
Referring back to SWA again there is no mention of special IR tests but GN3 page 34 states:
"Installation incorporating SWA will introduce parallel paths to protective conductors.
In such situations the R1+R2 test will need to be done prior to final fixing"
So there you go, there is no mention of special IR test procedures but R1+R2 is specifically mentioned so I guess you would have to remove the CPC from the board to test R1+R2 if the SWA had been already installed and the armour had been earthed.
It would be easier doing this way than trying to remove the armour earthing if you had a metal clad board.