yes mate i was trying to highlight the r1 + r2 part, i got the shock of my life when i read the examiners comments!
 
Last edited by a moderator:
Referring back to SWA again there is no mention of special IR tests but GN3 page 34 states:

"Installation incorporating SWA will introduce parallel paths to protective conductors.
In such situations the R1+R2 test will need to be done prior to final fixing"

So there you go, there is no mention of special IR test procedures but R1+R2 is specifically mentioned so I guess you would have to remove the CPC from the board to test R1+R2 if the SWA had been already installed and the armour had been earthed.
It would be easier doing this way than trying to remove the armour earthing if you had a metal clad board.
 
Last edited:
Referring back to SWA again there is no mention of special IR tests but GN3 page 34 states:

"Installation incorporating SWA will introduce parallel paths to protective conductors.
In such situations the R1+R2 test will need to be done prior to final fixing"

So there you go, there is no mention of special IR test procedures but R1+R2 is specifically mentioned so I guess you would have to remove the CPC from the board to test R1+R2 if the SWA had been already installed and the armour had been earthed.
It would be easier doing this way than trying to remove the armour earthing if you had a metal clad board.

did you do another test paper?

it will only introduce parallel paths if used a a cpc, if it has separate cpc then it wont introduce parallel path the the separate cpc.

think if the swa is cpc and its connected to metal conduit via gland, then when u measure the armour as cpc its adding the parallel paths, where if its a 3 core cpc, the cpc is not connected to the metal conduit!

i will try draw a pic
 
Referring back to SWA again there is no mention of special IR tests but GN3 page 34 states:

"Installation incorporating SWA will introduce parallel paths to protective conductors.
In such situations the R1+R2 test will need to be done prior to final fixing"

So there you go, there is no mention of special IR test procedures but R1+R2 is specifically mentioned so I guess you would have to remove the CPC from the board to test R1+R2 if the SWA had been already installed and the armour had been earthed.
It would be easier doing this way than trying to remove the armour earthing if you had a metal clad board.

well done mate i was reading up on that last night as well, gn3 giving reference to testing at various stages of the installation to avoid this exact situation
 
Maybe a special mention in the answer that the armour is not being used as CPC so need to disconnect it.

I mean in reality the armour is separated from the line conductor within by two sets of insulation, one covering the line cable and one covering the line neutral and cpc.
With all that insulation between the armour and the line I can't see how it would affect the results of an IR test and if it did you would want to know about it.
You would want to know if you had bad insulation between the armour and the line.
So it would be best to leave it earthed in my opinion.
But City and Guilds might see it different.
Do you see what i am getting at though, leakage from line inside cable to armour is kind of a parallel path because the armour is also earthed at the DB same as the CPC
 
Last edited:
Untitled-1.jpg

sorry its small and crap it was rushed, (and colours are wrong)
so the top image uses armour as cpc, you see when you do r1+r2 it will include the bonding to my fabulous pipe and back to the met, a parallel path.

the bottom image you can do the r1+r2 with the cores it will not include the armour just the cpc core and line core

make sense? hopefully there wont be a question on this!
 
i have only ever once tested well insulation on armour and that was a fault on an underground swa in a duct for street lighting - turns out the brown was damaged so i used black and grey for line and neutral (identification of conductors of course) and the armour as earth, made brown safe - lovely thought i was gonna be there all day lol
 

Reply to 2391 Odds and sods in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

I will offer some initial thoughts. A workplace so the EAWR 1989 applies, it is statutory and carries legal consequence drawing its authority for...
Replies
1
Views
237
  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top