I've been having a sort out on the computer and have found some 2391 past papers with answers, the following are questions 1 - 10 short answer and I'll post 11 - 20 in another thread in a bit. Not sure if it's an actual paper or one that has been put together.


City & Guilds 2391-10 Inspection & Testing 1
1 State three tests that may need to be applied to a ferrous enclosure, which forms the sole cpc for a circuit. (3 marks)
a) Continuity Test using a low resistance Ohmmeter to determine R2 or (R1+R2).
b) A continuity test using an A.C. Ohmmeter to determine R2.
c) An Earth Fault Loop Impedance test to determine Zs for the circuit fed by the ferrous enclosure.
2 State the effect on the insulation resistance of an installation if:
a) additional circuits are added
b) circuits were disconnected / removed
c) the length of a 6A lighting circuit was extended. (3 marks)

a) the insulation resistance value decreases.
b) the insulation resistance value increases.
c) the insulation resistance value decreases.

3 State:
a) why it is deemed necessary to remove one end of a bonding conductor connection when verifying its’ continuity
b) the instrument used to verify continuity
c) a typical value of resistance when verifying the continuity of bonding conductors. (3 marks)

a)to avoid false or inaccurate reading caused by parallel paths.
b) A Low Resistance D.C. Ohmmeter.
c)Less than 0.05Ω or negligible.


4 State FOUR external influences that you would need to consider during the inspection process. (3 marks)

Any FOUR from; Ambient Temperature, heat, water foreign bodies, corrosion, impact, vibration, flora, fauna, radiation, building use and structure.
5 State why it is necessary to verify the continuity of cpc’s prior to undertaking:
a) polarity tests

b) insulation resistance test
c) earth fault loop impedance test. (3 marks)

It is necessary to verify the continuity of cpc,s to ensure that the earth is present at a particular part of the installation.
a)A ‘dead’ polarity test is achieved by using the cpc as R2 in the Method 1 continuity test. Also, a ‘live’ polarity test is always measured between Live and Earth (cpc).
b)An insulation resistance test requires that we test to an earth as a reference, i.e. L-E, N-E.
c)The cpc (R2) forms part of the earth fault loop impedance path as shown in the formula Zs = Ze + (R1 + R2).


6 State FOUR prerequisite checks that need to be applied prior to undertaking an insulation resistance test. (3 marks)

i) verify that the supply is isolated
ii) any current using equipment is disconnected (loads or lamps removed)
iii) all switches and MCB’s closed and fuses in place
iv) disconnect and voltage sensitive equipment that may be damaged by the test.

7 State THREE types of installation that would be subject to Part 7 of BS 7671:2008. (3 marks)

i) Swimming Pools
ii) Saunas
iii) Marinas (or ANY from BS 7671:2008 Part 7).

8 State FIVE methods of Basic Protection. (3 marks)

i) insulation of live parts
ii) barriers
iii) enclosures
iv) placing out of reach
v) obstacles
9 Name the THREE electrodes used when employing a proprietary tester to measure the resistance of a rod type electrode.
(3 marks)
i)electrode under test
ii)potential electrode
iii)current electrode.

10 State the necessary test to be applied to a non-standard piece of equipment, which has been insulated on-site? (3 marks)

Utilising a ‘Standard Test Finger’ to IP XXB, connect a SELV supply not exceeding 50 V in series with a suitable lamp and connect between the test finger and the live parts inside the enclosure. The protection is satisfactory if the lamp does not light. Accessible top horizontal surfaces should also be tested for protection utilising a ‘Standard Test Wire’ to IP 4X.
 

Reply to 2391 Past Paper with Answers (Part 1) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
853
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
  • Question
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you...
Replies
0
Views
694
  • Question
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks