thats what i have been trying to find out eg if its a existing then I will include it say for a existing radial lighting circuit
seek permission to isolate supply
safely isolate supply, lock off ,circuit breakers off ,lamps removed,switches closed
use a approved gs38 voltage indicator to prove dead
check working on a known supply
check N-L, E-L, E-N & L-L at db for 3 phase
check instrument again to prove was working
select a low resistane ohmeter
confirm calibrated, condition, leads to gs38, set to low ohms scale
note resistance of leads or null
link Line and Cpc at DB with flying lead
test between L-cpc at all points on circuit and operate switches
record the highest reading at the furthest point as the (R1+R2)value for the circuit,
subtracting the resistance of leads if necessarry on the schedule of test results
remove test link,replace lamps
reinstate supply,turn CBs on