Hi all,
On friday I have the re sit for my 2391 practical, I'm confident on all the dead tests, Zs, RCD's and functional checks etc. And I'm fairly confident with the PEFC and PSCC, However on our test rig we have 2 boards (A main board, and a 'Garage' board) So do I need to do the PEFC and PSCC at both boards?
Thanks in advance.
 
I've just done my 2392. My understanding (and I'm sure I will be corrected if I have this wrong!), is that BS7671 requires the PFC (PEFC+PSCC) to be determined at the origin and at other relevant points. For simple installations, where all circuits eminate from the CU, that would be there. In the 'your' installation, the PFC should also be determined at the garage CU. My notes read that PFC should always be determined at the point of the installation where the electrical energy is deliverd. Only the same as for determining the ZS of those circuits.
 
Your main board should be supplying your garage board.

The main board is where the supply comes in to the installation. So you need to take Ze and PSSC/PEFC at that point.
You then have a submain from your main board supplying your garage board, this is a distribution circuit.
You have a choice, either measure Ze PSSC/PEFC at the garage board, and record the result as Zdb, or calculate them, whichever floats your boat.

Cheers..........Howard
 
Thanks all, I think finding the PEFC at the garage board should be alright, just do it as I would measuring the Zs but just press the PFC button. I assume the PSSC will be the same as for the main board. I just need to make sure I have the 'garage' breaker ON at the main board.....I think....
 
Thanks all, I think finding the PEFC at the garage board should be alright, just do it as I would measuring the Zs but just press the PFC button. I assume the PSSC will be the same as for the main board. I just need to make sure I have the 'garage' breaker ON at the main board.....I think....

Yep it's one of the live tests, before energising the garage circuits, test for PFC & PSC (record the worst figure, ie. the highest ka). The garage cu isolator will be in the off position, you are testing the distribution circuit from the garage CU back the house CU back to the supply transformer. Record as Zdb as Sirkit said (additional record of schedules & test reports to your EIC/EICR). You should carry out your garage CU ZS test before PFC tests.
 
Last edited:
Have a think about WHY you would do a PFC at the sub board and what you would use that result for (whether measured or calculated). It is not good enough to just record a result because the form has a box that needs to be filled in. There is a reason for this particular test.
 
The PSCC and PEFC should be at the highest at your main CU. With ohms law taking effect, the run to the garage will add more resistance to the circuit and so your PSCC/PEFC at the DB in the garage should be lower.
 
Like the other chaps just said, what is the relevance of the PFC an PSC, when would you get those currents? What would currents of that magnitude do? Would a low or high result be desirable? Answer those questions and you'll understand why you're doing it.
 
As far as I understand the reason we need to do the test is, to make sure that equipment (breakers) can cope with any potential fault currents. But thank you all for your help. I passed it today, and was very relieved to do so. AM2 in a few months time, so hopefully before long all the 4 years hard work will have an end product.
 

Reply to 2391 Practical re sit, Need a little bit of help... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
460
  • Question
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top