Hi, please i am studying for this and am starting to confuse myself,
1. Zs=Ze+(R1+R2) , (R1+R2) for radial and (R1+R2) for ring this I understand, but where do you get the R1+R2 for the distribution board (taking into acount that there are several circuits)
Live Tests
2.prospective earth fault current- remove main earth from MET and test on earth loop test against each phase incoming side of isolator - record highest reading. I believe this is correct.
3.prospective short circuit current - test between neutral and each phase record highest value and double record this on test sheet, I believe this is correct.
4.motor circuit - disconnect motor (R1+R2) on each phase or confirm continuety of conductors if on earth. if wired in SWA do you use the banjo/cable armour to do the R1+R2
Many thanks
 
Hi, please i am studying for this and am starting to confuse myself,
1. Zs=Ze+(R1+R2) , (R1+R2) for radial and (R1+R2) for ring this I understand, but where do you get the R1+R2 for the distribution board (taking into acount that there are several circuits). you don't. that is the Ze or Zdb for the board
Live Tests
2.prospective earth fault current- remove main earth from MET and test on earth loop test against each phase incoming side of isolator - record highest reading. I believe this is correct. no, you test Zewith earth dissed. PSCC with it connected to give the worst scenario.
3.prospective short circuit current - test between neutral and each phase record highest value and double record this on test sheet, I believe this is correct.
4.motor circuit - disconnect motor (R1+R2) on each phase or confirm continuety of conductors if on earth. if wired in SWA do you use the banjo/cable armour to do the R1+R2. if armour is used as cpc, then yes. if a earth conductor is used, then both are in the equation
Many thanks

my comments in red.
 
Hi, please i am studying for this and am starting to confuse myself,
1. Zs=Ze+(R1+R2) , (R1+R2) for radial and (R1+R2) for ring this I understand, but where do you get the R1+R2 for the distribution board (taking into acount that there are several circuits)
Live Tests
2.prospective earth fault current- remove main earth from MET and test on earth loop test against each phase incoming side of isolator - record highest reading. I believe this is correct.
3.prospective short circuit current - test between neutral and each phase record highest value and double record this on test sheet, I believe this is correct.
4.motor circuit - disconnect motor (R1+R2) on each phase or confirm continuety of conductors if on earth. if wired in SWA do you use the banjo/cable armour to do the R1+R2
Many thanks
1) if your on about the single phase sub board on the 2391 rig...then you would connect the line+earth/cpc on the sub cable at origin (3 phase panel)....and test between the 2 at the sub board....this would be R1+R2 for the sub...
2) correct...but dont forget to ask permission from the person ordering the test..or any other interested parties to isolate the supply (this would be the instructor)...safe isolation procedure and lock off....KEY IN POCKET...NOT LEFT ON THE TABLE...THEY WILL FAIL YOU FOR THIS......
3)you use the metal enclosure.....dont forget...an R1+R2 value you record should be the HIGHEST value aheaved....this would typically be between the line and an earthed metalic enclosure......such as a C/U...or panel....
 
Hi, please i am studying for this and am starting to confuse myself,
1. Zs=Ze+(R1+R2) , (R1+R2) for radial and (R1+R2) for ring this I understand, but where do you get the R1+R2 for the distribution board (taking into acount that there are several circuits) R1 and R2 refer to cables, not DBs, you measure them, usually by connecting the live and earth together at one end and measure continuity between both legs together at the other end
Live Tests
2.prospective earth fault current- remove main earth from MET and test on earth loop test against each phase incoming side of isolator - record highest reading. I believe this is correct. nearly.. leave the earth on the MET
3.prospective short circuit current - test between neutral and each phase record highest value and double record this on test sheet, I believe this is correct. Nearly, only double for TP ccts, some meters measure L-L anyway so no need to double and can test L-L
4.motor circuit - disconnect motor (R1+R2) on each phase or confirm continuety of conductors if on earth. if wired in SWA do you use the banjo/cable armour to do the R1+R2 - same as any other cct, if SWA has earth core and its terminated in DB, use that. If its using the armourings - use that.
Many thanks

WWWwwww
 

Reply to 2391 practicle advice please in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
954
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top