Hi Guys, going through some past papers and my brain won't work this one out any help appreciatted,

Single phase power circuit with a full load current of 25A circuit is installed using 6.0mm2 copper conductors with a circuit length of 35m. (give Resistance of 6.0mm2 copper is 3.08megohm/metre)

Q/ The line and nuetral combined resistance for the circuit is 0.26ohm, determine whether the circuit meets voltage drop requ. if the voltage drop to local db is 4.5V?

Help me please!!
 
sorry to much revision i think the correction is microhm per metre still happy to be corrected and chances are I'm wrong!!
 
Upvote 0
i,d have thought milli not micro. small "m" is milli
 
Upvote 0
It is milliohm for sure.

So with a VD of 4.5V to this DB, this leaves a permissable additional VD of 7V the max being 5% of 230V = 11.5V.

Using the values you have given above, with the resistance per meter being for both L&N conductors the formula is - L x Ib x R / 1000 = 35M x 25A x 0.26ohms / 1000 = 0.23V.

So total VD = 4.5V + 0.23V = 4.73V. The circuit complies.
 
Upvote 0
Is the formula not 2 x L x Ib x R / 1000

Where R = 3.06 mOhms / M

This gives me 2 x 35 x 25 x 3.06 / 1000 = 5.355 V + 4.5V = 9.85V

Although the values in the question don't quite tally up

ie circuit length L + N = 2 x 35 M = 70 M

Given R1 + R2 = 0.26 ohms

Therefore mOhms/M should be 0.26 / 70 x 1000 = 3.714 mOhms/M which in turn gives a figure of 7.43 mV/A/M.

Think the tabulated value for 6mm is 7.3 mV/A/M so this is slightly over.
 
Last edited by a moderator:
Upvote 0
Why would it be 2 x length mate??? as he states in the question that the line & neutral combined resistance is 0.26ohms which should equate to the milliohm/meter value.

As I said I used the values he gave which as you say dont quite tally up but I didn't have any literature to hand to check.
 
Upvote 0
The total circuit length is 35M from source to appliance so the total cable length of L + N is 70M or 2L when using the mOhms/M figure of 3.08.

Using the figure of 0.26 ohms overall resistance the formula is

Vd = Ib x R

Vd = 25 x 0.26

Vd = 6.5V

This is probably the way that the examiner wanted it answered as the original Vd was 4.5V + the additional Vd of 6.5V equals 11V which is just below the max.

Using the tabulated value for a 6mm of 7.3 mV/A/M you get

7.3 x 25 x 35 /1000 = 6.39V

I just wish C&G would research their questions correctly and have all values corresponding to each other so it could be worked out each way and get the same result.
 
Upvote 0
Ohms law Vd= IR
Vd= 25 x 0.26
Vd= 6.5V
6.5V + 4.5V= 11V. Just complies
They try and throw you off the scent by adding circuit length in there when it's not really needed as resistance has been calculated for you.
 
Upvote 0
The question gives a bit more info than is needed for this part - maybe other parts of the question refer to the theoretical value. I would use the given figure of 0.26 Ω as simple simon said (now what does that remind me of?), it's not really surprisising that a calculated figure is is slightly lower. Circuit just passes at 11V.
 
Upvote 0
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
2391 Question
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
parm,
Last reply from
pushrod,
Replies
12
Views
2,389

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top