Hello people.
I am studying my 2391 and have a question.
I can't seem to find the answer to it anywhere.
It is:

List in the correct sequence the first three tests to be carried out on a new circuit supplying a three phase kiln.

Guidance note three is great at listing tests for single phase and all my other books have plenty of single phase test explanations but I am finding it hard to get good information on three phase testing.
Can anyone recommend a book for me?
Or maybe a few links to good threads.
Thanks.
 
Hello people.
I am studying my 2391 and have a question.
I can't seem to find the answer to it anywhere.
It is:

List in the correct sequence the first three tests to be carried out on a new circuit supplying a three phase kiln.

Guidance note three is great at listing tests for single phase and all my other books have plenty of single phase test explanations but I am finding it hard to get good information on three phase testing.
Can anyone recommend a book for me?
Or maybe a few links to good threads.
Thanks.

Well, is there a specific test that is only carried out on a 3-phase circuit?

Where in the testing sequence does that test fall?

In other words, the sequence for single phase and 3-phase is identical until you reach phase rotation.

so your answer will be:

1 Continuity of protective conductors

2 Insulation resistance

3 Polarity
 
Well, is there a specific test that is only carried out on a 3-phase circuit?

Where in the testing sequence does that test fall?

In other words, the sequence for single phase and 3-phase is identical until you reach phase rotation.

so your answer will be:

1 Continuity of protective conductors

2 Insulation resistance

3 Polarity

I'd second that.
 
Thank you people.
I am going through past exam papers as I think this is the best way to practice for the exam and also the best way to get things to stick in my memory.
I will no doubt have some more questions in the future so please be patient.
Thanks.
 
Last edited:
Ok here's one that has been puzzling me.

State three different examples of a limitation that may be agreed with a client which is NOT already stated on the periodic inspection report.

And I know this one will be obvious to most of you but is the series of tests on a new radial circuit.
1. Continuity of CPC.
2. Insulation resistance.
3. Polarity.

And one more thing.
Why is it on page 103 of the OSG table 2D the maximum permissible measured earth fault loop impedance for an RCBO to BS EN 61009 such a low value.
I thought for RCBO's the earth fault loop impedance would be allowed to be very high, for 30ma RCBO 1667 Ohms.
I mean surely an RCBO behaves the same way as an RCD during an earth fault so how come these value are so high in this table.
The formula Z<50V/Ia springs to mind.

Thanks.
 
Limitations can be:The percentage of sampling.An item(s) of equipment that can not be isolated.No testing of luminaries over a certain height.Your sequence is correct and yes, you can use the 1667 Ohm maximum value as disconnection time is achieved by the RCD part of the device.
 
Yeah,

Agree with posts. The 2391 is about understanding inspection and testing, single phase or three phase, fundamental principles. Happy revision.
 

Reply to 2391 question. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
519
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
I think the point made here on knowing the calculations for verification of results etc is a good one. With one question leading onto the next not...
Replies
18
Views
1K
S
The coding part is all down to experience and knowing whether something is right or wrong. Remember some pics have no faults.
Replies
2
Views
325

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top