Procedure for testing
Lock off procedure
· isolate installation
· lock off and place key in pocket
· post warning notices
Prove dead as per GS 38 recommendations:
· Select an approved voltage tester that conforms to GS 38 requirements
· Use a proving unit to ensure correct operation of test lamp
· Apply test lamp to supply terminals to prove dead
· Re-use proving unit to check, test lamp operation
Continuity of protective conductors including main and supplementary bonding
R1 + R2 METHOD 1
· Select a low resistance ohmmeter
· Check condition of instrument
· Check the meter is within calibration date
· Check the instrument is zeroed
· Check the condition of the leads and probes
· Check that the resistance of the leads and probes is nulled out
· Connect the line conductor to the protective conductor at the distribution board
· Test between line and earth terminals at each outlet in the circuit
· If there is any light switches in circuit, operate them also include strappers into test
· Record highest reading at the circuits extremity this will be R1+R2
Long lead method
· Connect one terminal of the continuity tester to the installation main earth terminal
· Connect the other lead to the circuit protective conductors at various points in circuit
Main protective bonding conductors
· Disconnect the main protective bonding conductor at the water/gas supply or structural steel end
· The reason for this is to avoid parallel paths
· Connect the continuity tester to the main earth terminal
· Connect the continuity tester via a long lead to the end of the disconnected main protective bonding conductor, where situated at the gas/water supply
· The reading should be no more than 0.05Ω
Continuity of ring final circuit conductors
· Step1
· Disconnect ring circuit at distribution board
· Measure end to end resistance ( L-L ) ( N-N ) ( E-E ) and record results
· Step 2
· Connect the incoming line conductor of outgoing neutral conductor
· Connect the outgoing line conductor to incoming neutral conductor
· Draw a table and record results of the resistances at each socket between line and neutral (including spurs)
· Step 3
· Connect the incoming line conductor of outgoing earth conductor
· Connect the outgoing line conductor to incoming earth conductor
· Measure and record the resistances at each socket between line and earth (including spurs)
· Record results in table
· This has the benefit of giving a R1+R2 reading
· Confirm results by calculation from end to end resistances readings
· For step 2 ( L+N / 4 )
· For step 3 ( L+E / 4 )
Lock off procedure
· isolate installation
· lock off and place key in pocket
· post warning notices
Prove dead as per GS 38 recommendations:
· Select an approved voltage tester that conforms to GS 38 requirements
· Use a proving unit to ensure correct operation of test lamp
· Apply test lamp to supply terminals to prove dead
· Re-use proving unit to check, test lamp operation
Continuity of protective conductors including main and supplementary bonding
R1 + R2 METHOD 1
· Select a low resistance ohmmeter
· Check condition of instrument
· Check the meter is within calibration date
· Check the instrument is zeroed
· Check the condition of the leads and probes
· Check that the resistance of the leads and probes is nulled out
· Connect the line conductor to the protective conductor at the distribution board
· Test between line and earth terminals at each outlet in the circuit
· If there is any light switches in circuit, operate them also include strappers into test
· Record highest reading at the circuits extremity this will be R1+R2
Long lead method
· Connect one terminal of the continuity tester to the installation main earth terminal
· Connect the other lead to the circuit protective conductors at various points in circuit
Main protective bonding conductors
· Disconnect the main protective bonding conductor at the water/gas supply or structural steel end
· The reason for this is to avoid parallel paths
· Connect the continuity tester to the main earth terminal
· Connect the continuity tester via a long lead to the end of the disconnected main protective bonding conductor, where situated at the gas/water supply
· The reading should be no more than 0.05Ω
Continuity of ring final circuit conductors
· Step1
· Disconnect ring circuit at distribution board
· Measure end to end resistance ( L-L ) ( N-N ) ( E-E ) and record results
· Step 2
· Connect the incoming line conductor of outgoing neutral conductor
· Connect the outgoing line conductor to incoming neutral conductor
· Draw a table and record results of the resistances at each socket between line and neutral (including spurs)
· Step 3
· Connect the incoming line conductor of outgoing earth conductor
· Connect the outgoing line conductor to incoming earth conductor
· Measure and record the resistances at each socket between line and earth (including spurs)
· Record results in table
· This has the benefit of giving a R1+R2 reading
· Confirm results by calculation from end to end resistances readings
· For step 2 ( L+N / 4 )
· For step 3 ( L+E / 4 )