Scenario
The building has its own supply and forms part of a 230 v TT System. Ze and PFC have not been measured. All circuits are wired in 70 degree Celsius thermoplastic single core cables, with copper conductors, in surface mounted, galvanized steel trunking and conduit. All accessories, including the distribution board, are metal clad. All circuits are protected by type B circuit breakers to BS EN 60898 Apart from the socket outlet circuit and the lighting circuit which are protected by individual RCBOs to BS EN 61009-1. the main switch is a double pole 100 A, 300 A S-type RCD to BS EN 61008-1.
PLEASE SEE ATTACHMENT FOR DIAGRAMS.
QUESTION 1
The ring final circuit is to be tested prior to connection to distribution board.
A) explain in detail how the continuity of ring circuit conductors test would be carried out.
B) determine the expected results for each stage.
C) a test of external loop impedance is to be carried out to assess the effectiveness of the earth electrode. Describe how this test is to be carried out after safe isolation of the installation has been complet.
Please can someone help. Thanks
I think you need to have a go first rather than just ask for "help". What are you thoughts?
If someone just writes out an answer, how is that in any way shape or form going to help you?
Man you gotta get stuck in! Have a go, scan your attempt in, and you will get reams of help (and it will be useful help, the only time you learn is when you get it wrong)
no way mate wish they would make there minds up
thanks for the heads up as i have jsut done 2330 302 and it was one of my questions
because of 2391 i learned insulaton resistance ohmeter
now back to IR tester they are getting money for old rope
what are you testing and what test are you doingQuestion about the neon indicator!! Would I have to disconnect line + nuteral from the switch and connect together and then test?
Just started learning electrics. So if anyone as work on the 2394 exam?
Especial with fault finding results!!!!!!