I doubled the length of the conductors, but now I'm confused:
Table 4D1B in Appendix 4 states that 10mm sq cable in conduit drops 4.4mV/A/m at 70 [FONT=Tahoma, sans-serif]°[/FONT]C
The title at the top states:[FONT=Tahoma, sans-serif] 'Single-core ... cables', [/FONT]so I'd assume the values are for one conductor only.
The table in the question paper is different. 'Figure 1 below shows information on the
resistance of conductors in m
Ω/A/m.'
[FONT=Tahoma, sans-serif]The bottom row says nothing more than: 1m of a 10mm² conductor has a resistance of 1.83m[/FONT]
Ω at 20[FONT=Tahoma, sans-serif]°C.[/FONT]
[FONT=Tahoma, sans-serif]At 1amp, this gives a voltage drop of 1.83mV.[/FONT]
[FONT=Tahoma, sans-serif]The scenario also mentions
single cables in trunking and conduit.[/FONT]
[FONT=Tahoma, sans-serif]Sadly, when I compare the figures with BS7671, logic and common-sense cease to apply.[/FONT]
[FONT=Tahoma, sans-serif]The values on the exam paper should be the same as the values listed in BS7671, table 4D1B, but reduced a certain amount because they're at [/FONT]20[FONT=Tahoma, sans-serif]°C[/FONT][FONT=Tahoma, sans-serif] instead of 70.[/FONT]
[FONT=Tahoma, sans-serif]BS7671 says a 1m length of 10mm [/FONT][FONT=Tahoma, sans-serif]²[/FONT][FONT=Tahoma, sans-serif] cable drops 4.4V per amp,[/FONT]
[FONT=Tahoma, sans-serif]C&G say that the same cable drops 1.83mV.[/FONT]
[FONT=Tahoma, sans-serif]Temperature correction is 4% increase in resistance per 10[/FONT][FONT=Tahoma, sans-serif]°C[/FONT][FONT=Tahoma, sans-serif]increase in temperature, i.e. 20% for a 50[/FONT][FONT=Tahoma, sans-serif]°C difference.[/FONT]
[FONT=Tahoma, sans-serif]The difference in these two figures is 58%.[/FONT]
[FONT=Tahoma, sans-serif]What's going on? [/FONT]