did the exam last nite i thought the exam was not to bad still quite tough and the dreaded VD question came up by VD i mean voltage drop i think i managed to work it all out but i made the stupid stupid stupid mistake of saying it was within six percent instead of five dont know how heavily i will get penilised for that but was quite impressed with myself for being one of the very few to work it out dont get me wrong i did make a few more schoolboy errors on the exam too but fingers crossed got my practical on mon at 8am aarrgghh had a few beers last nite though how did the rest of you find it and what questions did you think were nuts cause i think there were a few
 
The question for volts drop went something like this
Determine the volt drop on this circuit and determine if this complies
With the regulations.

A circuit at 20 meters long
2.5mm cable
40 amp supply
7.41 from GN3

Solution:

mΩ/m x L
1000

= 7.41 X 20
1000

=0.148Ω

Using the VIR calculation

V=IxR

V=40x.0148
=5.92volts

Then 5% of 230 volts is 11.5volts

Therefore 5.92 volts is within the voltdrop of 11.5 volts

i think this is correct please confirm.
 
Upvote 0
i am not sure mate i just started to answer by calculating restance then X that by IB then X L divided by thousand think i completly trashed it came out with about 13.2v
thought it was something to do with V = IXR but wasnt sure only know how to do it by nv/A/M X IB X L divide 1000
hope someone got a test sheet out so i can have another look and learn how to work it out
 
Upvote 0
hi all
the question on how a fuse would be affected if connected in the neutral by

a). Overload
b).earth fault
c).Short circuit current

what was answer to this
 
Upvote 0
i answered that

i the correct dissconection time would not be achived
ii the earth fault protection would not operate correctly
iii the circuit breaker would still operate

dont know if this is corret though
 
Upvote 0
was it a fuse or cb, i answered something like

i) the circuit breaker would operate leaving line at full voltage
ii) the circuit breaker would not operate leaving line-earth at full line voltage
iii) the circuit breaker would operate
 
Upvote 0
your answer to i may be incorrect as the circuit breaker has operated in the event of a fault there would be no voltage present i think
 
Last edited by a moderator:
Upvote 0
i thought because it was in the neutral it only breaks the neutal so anything upto that point would still be live

i couldnt understand what they where asking in a few questions . The way they word things just confused me there were a lot of sneaky ones

i think if i sat that same exam again i would still struggle i dont feel confident in passing
I flew through then went back over it a few times and there was one that i think i had answered wrong and had to rewrite it at the end the volt drop one just completly boxed me. it was all the two things for this two methods for that they speak complete and utter jargon

do you have exam success and past papers as a lot of this never even came up did it
and a lot out of GN3 didnt come up
 
Last edited:
Upvote 0
Question on fuses was...

A. Fuse element breaks.
B. No effect on fuse element
C. Fuse element breaks


To add detail about what would still be live was irrelevant... but, in both cases there would still be a live voltage up to the point of the element.

Regardless, question asked effect of fuse.... no more detail, not worth risking adding detail that could be wrong.
 
Upvote 0
Question on fuses was...

A. Fuse element breaks.
B. No effect on fuse element
C. Fuse element breaks


To add detail about what would still be live was irrelevant... but, in both cases there would still be a live voltage up to the point of the element.

Regardless, question asked effect of fuse.... no more detail, not worth risking adding detail that could be wrong.


Not sure if I will get marks but I put A breaks B none C breaks
 
Upvote 0
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
2391 written exam last nite
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
62
Unsolved
--

Advert

Thread statistics

Created
bobby101,
Last reply from
mag8485,
Replies
62
Views
7,913

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top