So then, the mist is clearing and an image is appearing before me, yes, I think the memory is returning....
11. A ring final circuit has been installed and the continuity of its conductors successfully verified. State THREE outcomes and/or results to be recorded on the Schedule of Test Results. (3 Marks)
12. A test for the continuity of a protective conductor connecting the metallic gas service to the main earthing terminal during an initial verification is to be carried out. State the
a) Instrument to be used (1 mark)
b) action to be taken regarding the conductors (1mark)
c) action to be taken regarding the resistance of the test leads (1 mark)
13. State the earth return path, external to the installation, for EACH of the following systems
a) TN-C-S (1 Mark)
b) TN-S (1 Mark)
c) TT (1Mark)
14.State what happens to the value of insulation resistance when
a) the circuit length is increased (1 Mark)
b) the circuit length is decreased (1 Mark)
c) an installation is measured as a whole instead of the individual circuits (1 Mark)
15. List THREE different types of equipment which will require special consideration when carrying out insulation resistance testing, excluding dimmer switches (3 Marks)
16. State, from the formula Zs = Ze + (R1 + R2), what is represented by
a) Zs (1 Mark)
b) Ze (1 Mark)
c) R1 + R2 (1 Mark)
17 State the
a) purpose of the IP coding system (1 Mark)
b) level of protection provided by
(i) IPXXB
(ii) IP4X (2 Marks)
18. State THREE practical situations where BS7671 requires the use of an RCD with a maximum residual operating current of 30mA (3 Marks)
19. When using an RCD in a circuit forming part of a TT system, the following condition must be fulfilled: ZsI-delta-n is < or equal to 50V
a) state what is represented by I delta n (1 Mark)
b) Calculate the maximum permitted earth fault loop impedance for a circuit incorporating a 100mA RCD (2 Marks)
20. A test to establish prospective fault current is to be carried out on a single phase installation. State the
a) TWO tests to be carried out at the origin of the installation in order to determine the prospective fault current (2 Marks)
b) condition which MUST be verified once the value from a) above is obtained (1 Mark)